Tool Talk Discussion Forum
OK I'm Confused..
D13
12-29-2006 06:07:59
The main panel has the ground and neutrals tied together. So should my remote sub panel have the two main hot bussbars, 1 neutral bussbar, and 1 ground bussbar? In other words, I need to divorve the ground and neutral in every subpanel and on every wiring leg?
I've got 1 sub in the garage with 4 wire 240 to it, but I better look at the neutral and ground - I be they're tied on whichever side the breakers want the hot wire to be.
John T
12-29-2006 12:24:12
 Re: OK I'm Confused.. in reply to D13, 12-29-2006 06:07:59
Yeppers, at any sub panels fed off the main breaker panel, the Neutral Buss and the Equipment Ground Buss are isolated from each other UNLIKE at the main panel where they are indeed bonded together. The Equipment ground buss would, of course, be bonded to the metal case of the panel. You would carry 4 wires to teh sub panel, 2 hots, 1 Neutral, 1 Equipment Ground.
John T
tech4
12-29-2006 07:32:56
In a sub-panel the neutral should be isolated or insulated from the ground bus. The ground can be connected to the metal panel but the neutral bus is isolated just like the hot wires from the metal panel and ground buss.