Tool Talk Discussion Forum
Electrical Question?
Robert in Md
12-27-2006 17:20:12
I,m tapping into a 220 single phase line. I want to add a 110 volt receptacle from one of the hot wires. I know to tap from one of the 110volts wires. My guestion is, do I connect both the 110 volt neutral and ground wires to the 220 volt neutral wire. I,ve done this before but have forgot what I did. I know this is probably not to code but will it work. I,m not going to be using both circuits at the same time.
tech4
12-28-2006 15:37:11
 Re: Electrical Question? in reply to Robert in Md, 12-27-2006 17:20:12
I would like to know a little more about what you have and what you are trying to do. Is this location in your house or barn or at a well pump? How many wires do you have at the termination point? Is this a temporary one shot deal or do you need a permnant installation? Maybe if we hear all the information that there may be an easy answer or again it may require a lot of re-wiring and additions to have a safe installation.
MikeCatthemuseum
12-28-2006 05:10:07
Another solution would be to install an auxillary breaker panel. Just run your 220 into the panel and through a main breaker. You can then SAFELY install a 110 breaker and wiring suitable for your outlet, or up to a half dozen or so of them. You can also install a couple of 220 breakers in place of a couple of the 110s.
These little panels are cheap adn very easy to install. That's the safe and right way to go at it.
D13
12-29-2006 06:07:59
 OK I'm Confused.. in reply to MikeCatthemuseum, 12-28-2006 05:10:07
The main panel has the ground and neutrals tied together. So should my remote sub panel have the two main hot bussbars, 1 neutral bussbar, and 1 ground bussbar? In other words, I need to divorve the ground and neutral in every subpanel and on every wiring leg?
I've got 1 sub in the garage with 4 wire 240 to it, but I better look at the neutral and ground - I be they're tied on whichever side the breakers want the hot wire to be.
John T
12-29-2006 12:24:12
 Re: OK I'm Confused.. in reply to D13, 12-29-2006 06:07:59
Yeppers, at any sub panels fed off the main breaker panel, the Neutral Buss and the Equipment Ground Buss are isolated from each other UNLIKE at the main panel where they are indeed bonded together. The Equipment ground buss would, of course, be bonded to the metal case of the panel. You would carry 4 wires to teh sub panel, 2 hots, 1 Neutral, 1 Equipment Ground.
John T
tech4
12-29-2006 07:32:56
In a sub-panel the neutral should be isolated or insulated from the ground bus. The ground can be connected to the metal panel but the neutral bus is isolated just like the hot wires from the metal panel and ground buss.
Stan in Oly, WA
12-28-2006 09:08:00
 Re: Electrical Question? in reply to MikeCatthemuseum, 12-28-2006 05:10:07
Hi Mike,
I don't quite understand the solution you propose unless you're assuming that the 220 conductor is already the 4 wire configuration. Otherwise, wouldn't you have to use the ground as the neutral in the new sub panel, and incur all the crossover problems that most of the previous posts warn against?
All the best, Stan
MarkB_MI
12-28-2006 04:56:07
How do you know the "neutral" is really a neutral? If it's a four-wire setup, then it's no big deal; you should connect neutral to neutral and ground to ground and you're done. If you have only three wires, there's a very real risk that the grounded conductor can't handle the current required to trip the breaker. This could cause the grounded conductor to burn in two, which would result in the problem that Gerald described.
Gerald J.
12-27-2006 20:05:43
As John T. says hooking neutral and ground together at the outlet works for a while. I've had to investigate and explain two deaths from that when the single neutral was broken. When that single wire breaks, the metal case of a tool has 120 volts when any tool in that outlet is turned on. You won't survive that, nor your kids. Wire it right or don't wire it at all.
Gerald J. Electrical Engineer.
Ozlander
12-27-2006 19:53:44
The real problem is that he said it was a 220 VAC circuit. It so, the white wire may not be a neutral, but one side of the 220 VAC circuit. Should be marked with tape or something, but tape falls off or get ignored. Then the new receptacle is another 220 VAC one.
John T
12-27-2006 19:23:12
Robert, This answer assumes a typical residential 120 240 volt single phase 3 wire service:
First of all ONLY the 110/120 volt branch circuit requires and makes use of the white Neutral (a grounded conductor), the 220/240 volt circuit DOES NOT REQUIRE OR USE ANY NEUTRAL, its line to line. A branch circuit to feed a 220/240 volt motor would carry the bare/green safety equipment ground, but it does not use or require any white Neutral since its ONLY 220/240 votls thats used.
Next: Its ONLY at the service entrance main panel where the Neutral Buss and the Equipment Ground Busses are bonded together NEVER AGAIN DOWNSTREAM AT ANY SUB PANELS i.e. if the main service entrance panel was used to feed a smaller sub panel at a remote location in the house or atatched garage, you would have to run 4 wires to it, 2 Hots, 1 White Neutral (grounded conductor), 1 bare/Green Safety Equipment Ground (grounding conductor) and at that sub panel the Neutral Buss and the Equipment Ground Busses would be seperate and isolated NOT re bonded.
That being said, if you want 110/120 volt at some location you need to use one of the hots and a white Neutral (grounded conductor) then the bare/green safety equipment ground if its a 3 wire grounding type receptacle. If its only a 2 wire receptacle, that would be a hot and Neutral.
NOTE AND CAUTION: DO NOT use the bare/green safety equipment ground (grounding conductor) to carry return current for use on 110/120 volt. Its a violation of the NEC and a safety issue. The bare/green equipment ground (grounding conductor) is only to provide a low impedance current path back to the panel to trip the breaker and save lives. The Neutral (grounded conductor) is intended to carry return current back to the panel i.e use a hot and neutral for 110/120 volts.
NOWWWWW WWW sure I know it will work and its been done and how the older ranges and dryers will work and feed 110/120 volts while using the bare/green safety equipment ground to carry return current Yeah Yeah Yeah, Blah Blah Blah I knowwwww wwww those two (Neutral and Ground) busses are indeed bonded together at the service entrance panel.
ALLLLL LL IM SAYING IS TO USE THE BARE/GREEN SAFETY EQUIPMENT GROUND (a grounding conductor) TO CARRY RETURN NEUTRAL CURRENT IS A VIOLATION OF THE NEC AND CAN CREATE A SAFETY HAZARD.
Its your house do as you wish but as a retired electrical power distribution design engineer (BSEE Purdue 1969) I only feel right to give you the proper, safe and NEC approved advise.
SOOOOO OOOOO OO if you need to tap off 110/120 thennnnn nnn you need a branch circuit that has a white Neutral (Cant Use the bare/green safety equipment ground per the NEC). If you require BOTH 110/120 and 220/240 THENNNNN the branch circuit requires FOUR WIRES, 2 Hots, 1 Neutral (for the 110/120), 1 Safety Equipment Ground
Best wishes, God Bless and yall have a safe n happy new year
John T
jerrycpp(WA)
12-30-2006 09:21:50
 Re: Electrical Question? in reply to John T, 12-27-2006 19:23:12
Thank you for an excellent and easy-to-understand explanation of white versus green/bare. My question is, from the main to the sub panel, can you just run the 220 volt black/red/white (3 wires = 2 hot, one neutral) and then install a new ground rod for the sub panel to replace the green/bare?
John T
12-30-2006 10:05:35
 Re: Electrical Question? in reply to jerrycpp(WA), 12-30-2006 09:21:50
The answer is NOOOOO OOOOO OOOOO OOOOO OOOOO O. If you drove a rod into mother earth at that sub panel VERSUS running the 4th bare/green equipment grounding conductor from the main panel YOU DO NOT HAVE A DIRECT LOW IMPEDANCE CURRENT PATH BACK TO THE MAIN PANEL TO TRIP A CIRCUIT BREAKER AND CLEAR A POTENTIALLY HAZARDOUS FAULT. Mother earth, depending on the moisture and mineral content and the grounding electrode quality, is NOT a good low impedance current path, therefore if say a steel cased grounded electric drill (that uses the 3 wire grounding plug) got shorted to a hot live phase wire and since that ground rod you drove is a high impedance path back to the panel, if you touched the case and were standing on moist earth or anotehr good current path back to the panel, YOU COULD DIEEEEE E.
You see the electricity is seeking a current path back to the service transformer (thats where the voltage difference is) and earth isnt a good path. However, if you run that 4th equipment grounding conductor from the main to sub panel (as we told you), it IS A GOOD LOW IMPEDANCE CURRENT RETURN PATH back to the transformer (to trip a circuit breaker to save your life) via the Neutral and Ground busses being tied at the main panel which is served by the transformer.
The reason the Neutral, at BOTH the pole or pad mount transformer, PLUS at the service entrance is tied to a grounding electrode (driven rods or water or gas pipes) to Mother Earth is to bring everything back down to a common zero reference. That driven ground rod you wanted to use simply DOES NOT suffice as a good return current path back to the panel to trip a circuit breaker to clear a dangerous fault.
RUN 4 WIRES TO THE SUB PANEL FOR 120/240 VOLT SINGLE PHASE 3 WIRE SERIVICE 2 Hots,,,,, ,1 Neutral,,,,, 1 Equipment Grounding Conductor.
RUN 3 WIRES TO A 120 VOLT LOAD 1 Hot, 1 Neutral, 1 Equipment Grounding Conductor.
Hope this helps
John T retired electrical engineer
Bus Driver
12-27-2006 18:57:38
The neutral, which is a circuit conductor- carries current- is grounded at the service panel and at no later or downstream point. The equipment grounding conductor is also grounded at the main panel, but carries current only in the event of a ground fault or a surge arrestor operating. If the neutral is broken and correctly wired, the circuit stops working. The end of the broken neutral toward the device has full circuit voltage on it at that time! But if the neutral and ground are interconnected (or the same conductors) downstream and the neutral and the ground are broken upstream, the external surface of all grounded devices and appliance on that circuit will have full circuit voltage on them. Simply making something electrical seem to work properly does not at all mean that it is safe!
paul
12-27-2006 18:25:07
The problem is the neutral wire completes the circut and the ground is there to protect you & the building & several safety devices from causing a fire or death. Don't know if that feature will _ever_ be needed so if you hook it up wrong, you won't ever know - until someone dies or something burns down. Then you know.
Doesn't matter if you use only one at a time, that is a non-issue.
Tying the neutral & ground wire together, (or interchanging them as you hope to do) with the modern devices that use the ground plug or GFI, etc. will now have every metal surface of your tools energised if some little thing goes wrong.
Just how it is in this century. Things have changed over the past 40 years. Our tools are safer, but wiring things up 'just so they work' now makes the whole system more dangerous.
Only responsible thing to tell you is to run a new 4-wire (hot, hot, neutral, ground) wire & do it right.
--->Paul
buickanddeere
12-27-2006 18:07:03
Can you afford a few feet of wire and have the peace of mind knowing you havn't made and are using a booby trap? Neutral and ground are not the same or inter-changable. Somebody else may later come along and "use both". Somebody will sooner or later end up with 120V on the ground circuit which is supposed to be a safety system and supposed to hold grounded items to near earth potential. Any livestock anywhere there are circuits fed from the same service transformer as this 120V "farmer fix" plug? All in all you are probably just joking with this question to see if somebody gets stirred up. I mean, who would go and do such as wiring mess?
PaMasseyBob
12-27-2006 18:18:51
 Re: Electrical Question? in reply to buickanddeere, 12-27-2006 18:07:03
You electrical type guys think you are so smart. A half inch size piece of copper pipe will work just as good as any 70 amp fuse in a disconnect.
buickanddeere
12-27-2006 18:43:38
 Re: Electrical Question? in reply to PaMasseyBob, 12-27-2006 18:18:51
We call those 1/2 inch jobs, "time delay" fuses. One hopes there is enough "time delay" to get away from the area before she blows.
jeffcat
12-27-2006 20:38:53
 Re: Electrical Question? in reply to buickanddeere, 12-27-2006 18:43:38
You got that straight. Try that with 480 3phase some time. You never knew so many sparks could come out of a fuse pannel!!!
Kevin Bismark
12-28-2006 15:31:12
 Re: Electrical Question? in reply to jeffcat, 12-27-2006 20:38:53
Funny when there is no electrical panel left, just some marks on the wall where it used to be, or open up the switch gear and most of the buss bars are gone with black marks all over the place, every once in a while in some of the big industrial places I go to I see that and a lot of the time it never blows the main in the building, usually lucky and no one was close enough to get burned, just a little hard of hearing for a while
Gerald J.
12-28-2006 18:11:28
 Re: Electrical Question? in reply to Kevin Bismark, 12-28-2006 15:31:12
240 will often burn away the metals on each side of an arc and self clear partly because during the zero crossing of the alternation there's time for the ionization to clear. But a 240 volt arc won't draw enouogh current to trip a breaker up stream.
At 480, the arc isn't self clearing and still doesn't draw enough current to trip a breaker or blow a fuse. I've heard of a wall sized 480 volt panel burning the whole thing as the arc traveled towards the power source.
I had a client that closed a 480 volt switch after checking the fuses. It started to buzz and he raised his hand to shut it off. It blew the door off before he got there and enveloped him in a cloud of copper vapor. Lots of burns, but his hand shielded his face. That one did blow the upstream fuses but they weren't current limit, but where super lag renewables and I was able to account for their delay by the amount of copper vaporized.
I've run into electricians working in a plant with both 240 and 480 and if the boss asked them to work on 480, they waved a scared arm at him and told him where he could go (he could go work on the 480 himself) and didn't work on the 480.
Gerald
buickanddeere
12-29-2006 21:51:53
 Re: Electrical Question? in reply to Gerald J., 12-28-2006 18:11:28
347/600 around here in industry. Seems to be a lot of people who stand in front of a disconnect and use thier right hand on the lever??? We had a little oops with a 240/416 5000amp service at Young and Eglington in Toronto spring of 1988. Somebody tried to jam a new style fused disconnect into the switch gear designed for an older switch design and frame/rack. The 1st blast wasn't too bad and the guys ran like scared rabbits for the vault door. After a bit of arcing the tech cable jumpers used to supply additional switch gear failed. There was enough thrust from magnetic force it pushed the copper inside the cables right through the insulation. And shoved the conductor into the switchgear framework. The jumpers and buss bars were gone, copper and steel was splattered on the walls. Doors and panels were blown off the sides of the switchgear. It even blew the glass out of the electical meters. Would not have been so bad if some genious had not dis-abled the ground fault detection and protection circuit. It had been jumpered out temporarly to eliminate niusance trips. Years later the repair still had not been made of the GFD jumper removed. The busted battery backup emergency exit light I had complaine dabout weeks before. Was suddenly replaced within hours of the blast. We shut down TV Ontario for 36 hrs and had 27 Emergency Vehicles parked around the scene. Shut down the subway trains and delayed the Canadian Tire specials advertisment flyer too.