Welcome! Please use the navigational links to explore our website.
PartsASAP LogoCompany Logo (800) 853-2651

Shop Now

   Allis Chalmers Case Farmall IH Ford 8N,9N,2N Ford
   Ferguson John Deere Massey Ferguson Minn. Moline Oliver
 
Marketplace
Classified Ads
Photo Ads
Tractor Parts
Salvage

Community
Discussion Forums
Project Journals
Your Stories
Events Calendar
Hauling Schedule

Galleries
Tractor Photos
Implement Photos
Vintage Photos
Help Identify
Parts & Pieces
Stuck & Troubled
Vintage Ads
Community Album
Photo Ad Archives

Research & Info
Articles
Tractor Registry
Tip of the Day
Safety Cartoons
Tractor Values
Serial Numbers
Tune-Up Guide
Paint Codes
List Prices
Production Nbrs
Tune-Up Specs
Torque Values
3-Point Specs
Glossary

Miscellaneous
Tractor Games
Just For Kids
Virtual Show
Museum Guide
Memorial Page
Feedback Form

Yesterday's Tractors Facebook Page

  
Tractor Talk Discussion Board

Re: OT Wiring Syrup tank


[ Expand ] [ View Replies ] [ Add a Reply ] [ Return to Forum ]

Posted by John T on August 18, 2006 at 06:34:21 from (66.244.90.5):

In Reply to: OT Wiring Syrup tank posted by J - IA on August 17, 2006 at 19:10:14:

J IA, First of all you definitely wanna go with 240 volts if the motor is a dual voltage 120/240 or more likely a straight 240 volt for a 5 HP. Thats a decent sized motor for single phase application you know. Next, Ugly's Electrical Refernces Handbook lists 28 amps as the full load current for a 5 HP Single Phase Motor at 230 V.

Soooooo assuming its a 240 volt single phase motor I strongly suggest you use 8/2 with Ground (3 conductors, 2 insulated phase wires plus a bare or green insulated equipment ground) Type UF (Underground Feeder) Cable. Unless its a very long run (how far is it???) in which case you might need larger gauge wire to reduce voltage drop, but at 28 amps the 8 Gauge ought to be adequate for a long distance. NOTE: I would NOT try n get by with 10 Gauge Wire..........

Once you get to the Motor I would use a 2 pole (NEMA 1 Enclosure if indoors NEMA 3R if Outdoors) Safety Switch Disconnect right at the motor but at worst case in sight and within 50 feet from it. You can choose either a 2 pole fuzed or circuit breaker type of Safety Switch Disconnect for the Motor, and if a fused you might get by with a dual element time delay (Slow Blow) fuze or perhaps a 40 amp circuit breaker since motor start up current (approx 6 x run current) might trip a 30 amp breaker. You are permitted to size a motor service circuit breaker at a higher current rating then the Motors Full Load Amps (28) in order to allow for it to start as the Motors Internal Thermal Protection Current Overload (assuming it has a thermal overload protector) ought to trip out to protect the motor if she overheats or overcurrents. In the event the motor had no internal thermal overload protection, then you should use a regular motor combination starter (disconnect plus overload protection) to provde the disconnect PLUS overload protection. See if the motor has some sort of red pushbutton type of thermal overload?????

I would use a Rigid Conduit riser up out of the ground to the Safety Switch and then use watertight flexible conduit (Seal Tight) from the Safety Switch to the Motor. Dont forget to bond the bare/green safety equipment ground to the safety switch and conduit and the motor itself.

NOTE: I been retired a good while and am rusty on the NEC and havent kept up but believe most of the above to still be accurate but NO WARRANTY LOL

Best wishes n God Bless

John T Retired Electrical Engineer in Indiana


Replies:




Add a Reply

:
:
: :

:

:

:

: If you check this box, email will be sent to you whenever someone replies to this message. Your email address must be entered above to receive notification. This notification will be cancelled automatically after 2 weeks.


TRACTOR PARTS TRACTOR MANUALS
We sell tractor parts!  We have the parts you need to repair your tractor - the right parts. Our low prices and years of research make us your best choice when you need parts. Shop Online Today. [ About Us ]

Home  |  Forums


Today's Featured Article - Field Modifications (Sins of the Farmer) - by Staff. Picture a new Chevrolet driving down the street without it's grill, right fender and trunk lid. Imagine a crude hole made in the hood to accommodate a new taller air cleaner, the fender wells cut away to make way for larger tires, and half of a sliding glass door used to replace the windshield. Top that off with an old set of '36 Ford headlight shells bolted to the hood. Pretty unlikely for a car... but for a tractor, this is pretty normal. It seems that more often than not they a ... [Read Article]

Latest Ad: Sell 1958 Hi-Altitude Massey Fergerson tractor, original condition. three point hitch pto engine, Runs well, photos available upon request [More Ads]

Copyright © 1997-2024 Yesterday's Tractor Co.

All Rights Reserved. Reproduction of any part of this website, including design and content, without written permission is strictly prohibited. Trade Marks and Trade Names contained and used in this Website are those of others, and are used in this Website in a descriptive sense to refer to the products of others. Use of this Web site constitutes acceptance of our User Agreement and Privacy Policy

TRADEMARK DISCLAIMER: Tradenames and Trademarks referred to within Yesterday's Tractor Co. products and within the Yesterday's Tractor Co. websites are the property of their respective trademark holders. None of these trademark holders are affiliated with Yesterday's Tractor Co., our products, or our website nor are we sponsored by them. John Deere and its logos are the registered trademarks of the John Deere Corporation. Agco, Agco Allis, White, Massey Ferguson and their logos are the registered trademarks of AGCO Corporation. Case, Case-IH, Farmall, International Harvester, New Holland and their logos are registered trademarks of CNH Global N.V.

Yesterday's Tractors - Antique Tractor Headquarters

Website Accessibility Policy