This is a subject that has come up frequently but I never paid too much attention because it didn't concern me directly. Now I have a friend who needs to know this thing that I can't tell him. He is running sufficiently large cable from a 200 amp panel to a 70 amp sub-panel. What is the grounding requirement at the 70 amp location? I can provide more detail if necessary.
Thanks, Stan
dave guest
03-11-2008 17:25:03
 Re: Grounding sub-panel in reply to Stan in Oly, WA, 03-11-2008 12:44:40
In mich I have been told both by different inspectors in different communities. At a code seminar, it was stated thus, "call second panel a service, drive ground rods, ground neutral in panel. Call second panel, feeder, isolate neutral and add fourth wire." I would absolutely call inspector on this. That's their job. Many things in electrical do change over time. New work should be up to the latest code to protect owner and have insurance underwriters happy or they may not satisfy you in event of problem.
504-2
03-11-2008 16:59:33
Have fun in Moline, the wife and I went through the museum Sunday afternoon, quite a place. BTW the steak house just west of the museum is excellent. Kevin
paul
03-11-2008 15:54:02
Typically the 4 wires and _not_ bonded in the sub panel as others say.
Depending on local code & if this is 2 seperate buildings and no shared plumbing & if considered agricultural, they allow a 3 wire, no ground wire between, service. Maybe. It's something to look into local code if the price diff is a lot. With this, both panels would be ptreated like a main panel, both with ground rods, both with bonded neutral/ground buss. This would depend alot on your local inspector, the ag exception is in the rules, but somewhat gray area.
--->Paul
John T
03-11-2008 15:05:55
Stan, Myself, a too long retired n rusty as an old nail electrical engineer and a current active NEC Inspector have covered this ad nauseum over on Johnnypopper in the Potbellied Stove Forum n Im too tired n limited for time to do it alllll l again lol. However, if hes running from a panel to a sub panel in the same building HE MUST CARRY ALL 4 WIRES: 2 Hots,,,,, 1 Neutral (a grounded conductor), 1 Equipment Grounding Conductor.
FURTHERMORE at that sub panel and UNLIKE at the main service entrance panel THE NEUTRAL BUSS AND THE EQUIPMENT GROUND BUSSES DO NOTTTTT TTTTT BOND TOGETHER. THEY REMAIN SEPERATE N ISOLATED FROM EACH OTHER. His incoming Neutral (White) obviously goes to his sub panels Neutral buss while his incoming Equipment Ground (bare/green) goes to the sub panels Equipment Ground Buss. The sheet metal of the panel would bond to the equipment ground buss not the Neutral of course
The wire sizes depends on the amps and length of run. We did NOT use any additional grounding electrodes (driven rods or water pipes or building steel etc) at the sub panels in the same buildings.
Headed to Moline Illinois to speak at the John Deere Gathering of the Green Conference, see yall soon
John T
buickanddeere
03-11-2008 14:37:26
How long is the cable between the 200amp & 70 amp panel? Is buddy conecting to a breaker inside the 200amp panel? Or direct to the buss bars? I agree, two 10ft ground rods 10+ ft apart and bonded together with #6 copper at the sub panel.
Sparktrician
03-11-2008 13:10:53
Your friend will need to run 4 wires to his sub panel. 2 hots, 1 nuetral, 1 ground. The ground to run from the ground bus in main panel to ground bar in sub panel. DO NOT BOND THE GROUND AND NUETRAL IN THE SUB PANEL!!!! You will need a ground bar kit for the panel you are installi ng. Also, do not install bonding screw in the nuetral bar. You may want to drive a ground rod for the subpanel, just for good measure. Not code required (in my area) but when feasable, i usually do. If you give me some distances involved i can size the wire for you. Good Luck.
Stan in Oly, WA
03-11-2008 15:25:35
 Re: Grounding sub-panel in reply to Sparktrician, 03-11-2008 13:10:53
Sparktrician and buickanddeere,
Thank you both for the information. I'm going over to take a look at my friend's setup in a week or so. He knows so little about it that it's difficult to find a common language to ask questions about what he has. The 70 amp sub-panel has been in place and in use for 5 years. What my friend can tell me about it for sure is that the distance involved is 250', and there is no grounding rod at the sub-panel location. He says that the cable between the two panels is #2 aluminum. He may mean 2/0, but I won't know until I see it.
My guess is that my friend got reasonably good advice about the installation 5 years ago, and now he doesn't remember enough about what was done then to even talk about it in terms that tell me much. I think he will do what needs to be done or spend what needs to be spent to correct any problems that could endanger others, and that's about it.
Thanks, Stan
John T
03-11-2008 16:17:22
 Re: Grounding sub-panel in reply to Stan in Oly, WA, 03-11-2008 15:25:35
Stan, Now Thisssss sss is a totally differernt situation""""" """"" " Normally when we speak of "sub panels" we were thinkin a sub off the main in the same building..... ...If its a seperate building away from n isolated from the other and theres nooooo ooooo o common connecting metal water or gas pipes and no connecting bonded communication lines etc then its possible to ONLY carry three wires (2 Hots and a Neutral) out there and once there its like its own and just another derived source from the utility. In that case YESSSSS SS you need grounding electrodes such as made ones like one or two driven ground rods (per local inspection authority regulations) and/or building steel and metallic water pipes. However, if metalic water pipes connect n bond to the two buildings and they are bonded to the electrical system (as/if required) then go back above to the 4 wire rules n follow them.
This can be tough over the net not being there to observe the actual conditions, best consult a local engineer or electrician is my best advice, electricity can killlll lll if the installations isnt correct.....