Tool Talk Discussion Forum
I Think I Need a Relay��.
Scott.ID
03-05-2008 00:58:21
But I�m not sure what kind. Maybe some of you could help me out.
I built a new shop, and my compressor is on the far wall away from the entrance door. While planning the electrics for the shop, the elec inspector recommended I put a switch by the door so I could break one leg of the 220/240 and turn the compressor on/off whenever I come in or go out.
I ran 10/4 from a dbl 30A in the breaker panel over to the box for the compressor. I also ran 12/2 w/g (his idea) from the same box up thru the ceiling, over to the door, and down to the switch box. The length of the 12/2 is about 40 ft. I installed a 20A switch in the box and connected the black to one lead and the white (with black tape) to the other switch lead.
I�ve been using the 7hp compressor for 6 months now without the switch hooked up, but it was a loose end so I figgered I�d finish it up. I broke one 10/4 hot lead in the compressor box and spliced in the 12/2 leads from the switch by the door. Now I have to cycle the switch several times if I want to start the compressor and I�m afraid I�m going to burn something (the motor) up every time the compressor tries to cycle up.
I�m sure that the 80 ft of 12 ga is what�s killing me. Is there some type of Relay I can mount behind the compressor that can break the 2 hot 10/2 leads and be controlled by the 12/2 switch? I have a separate 120 outlet within 3 feet if I need power. I forgot to mention the walls are finished so running a larger line to the switch is out of the question.
Ideas? Theories? Sorry to be long winded, but I wanted to give you as much info as I could. Cheap is good, but safety rules!
Scott
olddog
03-09-2008 05:29:59
 Re: I Think I Need a Relay��. in reply to Scott.ID, 03-05-2008 00:58:21
Did yer inspector say" break one leg to the COIL of the contactor"? For 7 HP you already have a relay (contactor).
KEB1
03-05-2008 19:20:30
Another relatively cheap option would be use a low voltage contactor like the ones used to turn air conditioning compressors on & off. These switch both sides of the line. Just make sure the contacts are rated to start whatever size motor you're using. They are normally rated for locked rotor amperes.
If you get one with a 24 VAC coil, you can use a standard HVAC transformer to make 24 volts, switch the 24 volts with your wall switch, and let the contactor switch the compressor. You might also find one with a 120 VAC coil, in which case you wouldn't need the transformer.
Check with a local motor supplier, an electrical supply house, or a good HVAC supply company.
Keith
dave guest
03-05-2008 18:14:03
Always 2 pole switch on 220volt. Wire size also too small, the #12 that is. And fire the inspector.
El Toro
03-05-2008 17:44:55
I used No10 wire for a 3hp 240 volt compressor motor that draws 12 amps. If that's a 7hp motor and you divide 7 by 3= 2.333 X 12amps=27.998 amps.
You probably need at least 8 gauge wire.
I ran the wire about 30 feet from the main breaker panel to a disconnect in the garage and a wire from the disconnect to a receptacle in the basement that accepts the male plug on the compressor. I can start and stop it from the garage. There's a 20amp breaker at the disconnect and one at the main breaker panel. Its been in use for 36 years. Hal
Dick L
03-05-2008 12:45:25
Hear Ya go. It is called conduit to rewire a screwup when the walls are finished in a shop your wife don't have to decorate.
Get this motor starter on ebay, put the correct heartes in it for the motor, mount it in a box. You can then use your 80 feet of 12 gage to engage the coil with a toggle light switch.
This would have the three lugs but you would only have to use the two.
Dick L
03-05-2008 13:11:01
 Heres Another Motorstarter in reply to Dick L, 03-05-2008 12:45:25
This has more information on the size 1 load capacity.
John T
03-05-2008 12:08:21
Scott,
At that compressor you need two things, One a safety switch/disconnect (and a two pole, DO NOT just open or switch one of the hot legs), Two some sort of motor thermal overload protection. Whats called a Combination Starter is both combined in one single unit.
If you desire some sort of a remote safety shut off then you can add some sort of a shunt trip circuit breaker with like a mushroom head push to kill switch controller at the remote location which opens the breaker if its pushed
Another option to kill the compressor from a remote location is a TWO POLE contactor/relay with the control push to kill switch (similar to above) located by the door
AGAIN use a two pole switch to shut on/off the 240 volt motor DO NOT use a single pole
John T Long retired eolectrical engineer so a lil rusty on this stuff NO WARRANTY
Vern-MI
03-05-2008 10:30:49
One of these Motor starter disconnects would work good for your application With this you can throw the disconnect at the wall by the compressor and you can also interrupt the starter solenoid using your remote located switch. That way when you use the remote shut off you would be disconnecting the power to all three legs of your 220 VAC compressor circuit. I'm surprised that you haven't burned the one leg of the 220 VAC curcuit when you interrupted the other leg at your remote switch. Maybe I don't understand your particular system wiring.
caterpillar guy
03-05-2008 05:32:10
I would think the wire should be 8ga for that load all the way around.
Charles (in GA)
03-05-2008 05:26:41
Is this a REAL 7 hp motor? or one that has a 7 hp STARTING hp rating? which amounts to about 3 real hp (running hp is how motors are actually rated).
A 10 gauge wire is not enough (or marginal at best) for an actual 7 hp motor which would draw in the neighborhood of 28 amps. I'll bet the data plate on the motor says the FLC amps is about 15 to 17 amps.
With all of that said, as others have noted, if this is a real 7 hp motor it probably should have a motor starter box mounted on it.
The 12 gauge wire, is probably killing this system, if you want some sort of remote shutoff, it needs to be a relay operated, and if you have a motor starter, the circuit could be wired to control the relay, probably by interrupting the pressure switch/starter circuit.
Personally I think a trip across the shop, to turn off the air valve at the tank, and shut off the compressor (you DO have a disconnect at the compressor don't you?) is not too much to ask.
Charles
dr sportster
03-05-2008 05:45:06
 Re: I Think I Need a Relay��. in reply to Charles (in GA), 03-05-2008 05:26:41
Sorry I came out under Charles by mistake.Important point Charles has DONT YOU HAVE TO GO OVER TO THE TANK TO SHUT THE air VALVE OFGF ANY HOW.oops
dr sportster
03-05-2008 05:39:56
The diconnect only shuts off one leg!!?? Whats up with that? This only gives me more questions not answersStarter?Where are the overloads or heaters located?.Cant you just shut off at the unit? what protects the 12/2 circuit?Why is an inspector even givig advice to a layman.A disconnect must "disconnect" all power so the unit can be worked on.This is why you must always use your voltage tester[hardwired not tick].I would walk across my shop before I would spend.
DH in Carolina
03-05-2008 04:56:56
Here"s what I would do. If that is a 7 hp motor on that compressor you should have a motor starter on it with the pressure switch breaking the hot wire to the motor starter coil. I would run the 12/2 wire from the compressor to a swith at the door. Break the pressure switch , motor starter coil circuit with the 12/2 wire. Install a single pole switch at the door. This will stop the compressor without having the motor power having to travel over the 12/2 wire. DH
El Toro
03-05-2008 04:55:12
You had better get a licensed master electrician
to inspect what you have wired up. Hal
Joe(TX)
03-05-2008 04:48:00
The inspector does not know what he is doing. Why does it need a switch by the door. a switch at the comprssor will turn it off aand on.
For one thing, 12ga is not big enough to switch 30a. It still needs to be 10ga.
Don't ever just turn off one leg on 220.
Circus
03-05-2008 04:03:32
That inspector was wrong, burn in heII wrong. Forget the whole idea. It is required (code) to have a motor controller for large motors. It's basically a relay with heat sensor breaker etc. A remote switch wired in series with the pressure switch WHILE USING A CONTROLLER is do able. I'm no expert, your on your own.
MarkB_MI
03-05-2008 02:56:32
I really have to question the credentials of an "inspector" who recommends that you shut off a 240V circuit by switching one leg. That other leg is still hot! You need a double pole switch suitable for 240.
I don't understand why you ran 10/4. Maybe you mean 10/3, which has three conductors plus a ground. At any rate, 10/2 would be the correct cable for this purpose.
You are right that the 12 gauge wire is killing you. For that long of a run, you probably should have gone with 8 gauge. 10 gauge at the very least for a 30 amp circuit. Whatever you do, get that switch out of the circuit before you wreck your compressor motor or burn down your building.
CH(upstate,NY)
03-05-2008 02:42:08
Go to your electrical supply and get a 30 amp double pole contactor with a 120 volt coil. Gonna cost some bucks to save a few steps. If your load center is closer, I'd just throw the breaker.
Last I knew, you can't use 20 amp wire and devices in a 30 amp circuit.
CH(upstate,NY)
03-05-2008 02:45:54
 Re: I Think I Need a Relay��. in reply to CH(upstate,NY), 03-05-2008 02:42:08
Also, if you pull the 120 volt for the switch from the 220 at the compressor, you would have to fuse that line for 20 amps.
T_Bone
03-05-2008 05:00:37
 Re: I Think I Need a Relay��. in reply to CH(upstate,NY), 03-05-2008 02:45:54
Hi Scott,
As CH stated, you need to use a pilot circuit(operator, ie; switch, thermostat, etc) to a contactor (load control). I would suggest a DT 40a, 120v coil contactor as they don't cost a couple dollars more but will last longer.
L1&L2 are lines in and T1&T2 are for load switching.
The pilot circuit has to be tied into the main disconnect of the load being controlled. This way the pilot circuit will be disconnected when the compressor is disconnected from the main.
T_Bone