Tool Talk Discussion Forum
Short run of electrical conduit
Stan in Oly, WA
01-22-2008 22:29:09
I have 200 amp electrical service and the breaker box is uncrowded because my range, dryer, water heater, and furnace are all natural gas. Recently I ran a line for a dedicated computer outlet (on its own breaker), and another new circuit for a few outlets along one wall in the living room. The new cables come out of the crawlspace through the wall about two feet below the electrical panel. Do the regular rules about the number of conductors per size of conduit apply when the run of conduit is this short, less than 30"?
Thanks, Stan
Charles (in GA)
01-23-2008 15:14:49
 Re: Short run of electrical conduit in reply to Stan in Oly, WA, 01-22-2008 22:29:09
Chapter 9, note 4, also covers the fact that a conduit 24 inches or less is a nipple and does not fall under the requirements of adjustment factors for number of conductors (as already mentioned)..... ..... ..... .... However..... ..
Chapter 9, Note 4 does specify a maximum fill of 60% of cross sectional area for nipples.
If this is romex, you must use the major diameter of the elipse as a circle diameter when calculating the conductor area. Chapter 9, note 9.
Charles
Bus Driver
01-23-2008 04:21:47
Adjustments for number of conductors in conduit do not apply to conduits that do not exceed 24" in length. NEC Article 310.15(B)(2)Exception No.3.
bill in in
01-23-2008 04:15:19
yep