Tool Talk Discussion Forum
Subpanel load-balancing question
Mattlt
10-29-2007 12:08:21
I'm having brain failure...
At work, we have a 100 Amp 240V subpanel feeding our computer room (single phase). We had an electrician come in to check the balance / utilization of the circuits. He left a note saying Phase A = 43 amps, Phase B = 36 amps.
Now, I'm assuming, given the 80% rule, we are slightly over on Phase A, and slightly under on Phase B.
However, this got me thinking. The subpanel has a 100 Amp main breaker (240V). Does this really translate to 50 Amps per leg of 120V? Assuming 80% of each leg is available, we'd really have 40 Amps available on each leg?
If it matters, this subpanel only feeds 120V circuits. Again, this is a computer room, constant load, no motors, etc.
Mattlt
10-30-2007 06:50:27
 Re: Subpanel load-balancing question in reply to Mattlt, 10-29-2007 12:08:21
Thanks for setting me straight. The boss is happy now.
buickanddeere
10-29-2007 15:40:05
It's a good idea to balance the lines and reduce the neutral current were practical. Sometimes nasty harmonics get circulating with spikes and out of phase wave from from electronic power supplies. On occasion the neutral can become "overloaded" even when the line currents are close to apparently canceling the neutral current. Sometimes either over size neutrals are required. Or an individual neutral per line is the solution.
Red Dave
10-29-2007 12:17:58
No, the 100 amp 240 volt breaker will permit 100 amps to each 120 volt leg. The two 120 volt legs are in series, with any difference carried by the neutral. The 80% rule would allow a constant load of 80 amps on each leg.
The reason for checking the balance is to keep neutral current within reasonable limits.
If you had 80 amps on one leg and no amps on the other, that would be a problem because the neutral would have to carry the difference, which is 80 amps.
43 amps on one leg and 36 amps on the other should be no reason for concern. The neutral is only carrying the difference, which is 7 amps.