Tool Talk Discussion Forum
12 ga. extension cords and 220 volts
Tim B from Ma
10-24-2007 14:10:22
I am wondering if it would be unsafe to use a 12 ga. extension cord (100 feet) to run a 220 volt compressor (7.4 amps).
I have two 12 ga extension cords, one is rated for 15 amps (???? they seem to be covering their buts with both hands) and 115 volts and the other just has a "20 amps" notation, no voltage rating seen.
At Home Chepo I see all their 12 ga cords are rated for 115 - 120 volts.
All my Romex wiring seems to be comfortable handling 600 volts (if I recall correctly).
Is this just because of the pattern and/or construction of the plug ends (and them covering the behinds for liability purposes), or is there a safty issue with running 220 volts through multi-strand copper 12 ga wire? All I can imagine is heat production which might melt the insulation.
Is 7 amps at 220 volts going to cause more heat than, say 13 amps at 115 volts?
Thanks,
Tim
Charles (in GA)
10-25-2007 17:10:42
 Re: 12 ga. extension cords and 220 volts in reply to Tim B from Ma, 10-24-2007 14:10:22
Lots of naysayers on this subject, but IH2444 has this right. 7.4 amps on 240v on a 12 gauge wire for 100 ft isn't much of anything. You do need to use the correct plug and receptacle on the ends of the cord however.
The cords were marked 15 amp because that is all a common 120v plug and receptacle is rated to, and thus becomes the limiting factor.
I have a 1hp Craftsman compressor, probably 35 years old, bought it new. When I built my shop it was a year before I got power on the building. For a year, a 100 ft long, 12 gauge, 120v extension cord lay in the yard running from an outlet on the back porch of the house out to the shop. That little Craftsman compressor shows something like 17 amps on the data plate, and it ran just fine on that cord, when it started the fluorescent trouble light also on the circuit would go out momentarily but I understood that, considering the amps I was drawing.
Charles
tatanka
10-25-2007 14:06:07
Dont use it. too much voltage drop when the aompressor is running. It will burn up the motor or start a fire
Tim B from MA
10-25-2007 11:33:18
Thanks for the replys gents.
Buying air hose rather than extension cords surely is the way to go - at those distances the most I am planning to do is use a framing gun.
I posted that question before I left work last night, then stopped on the way home at LoweDown and checked out air hose. I did not realize how cheap it is.
Still, good information in those posts - stuff I can surely use next time I need to do some dangerous kind of gerryrigging.
Joe(TX)
10-25-2007 05:33:56
They say 115-120 volt because thats what kind of plug they have.
JMS/.MN
10-24-2007 21:11:34
Go with paul's idea- hose is always better than extension cord. Keep the compressor close to the power source, and buy hose to run the air. Any cord will run 120 volts- that doesn't mean squat. It's the amps that count, along with the distance. Running a compressor on a long cord of insufficient size will simply overheat the motor, and burn it out. Air hose will not be overloaded.
paul
10-24-2007 19:54:07
Are you planning on cutting the ends off & putting 240v ends on it? That would be obvious - but you didn't mention that.....
$20 will get you 100 feet of hose, I'd go that route. Compressers don't like extention cords, they draw a lot of power to start up. Trips breakers real easy. Not sure you will find a 7 amp 240v breaker to protect that cord. ;)
--->Paul
John T
10-25-2007 07:13:05
 Re: 12 ga. extension cords and 220 volts in reply to paul, 10-24-2007 19:54:07
The NEC allows you to oversize a circuit breaker so as to allow for the high initial surge of motor start up current (which is about 6 x running current). The theory is the breaker will still protect against a short (to protect the feeders) while the motors thermal overload protection (internal or starter/heaters) is there to protect the motor..... .. One can also use fuses versus circuit breakers for sizing and the use of dual element time delay devices allows for the initial short surge of higher (then fuses rating) start up current.
Sufficiently large air hoses (to avoid excess pressure drop) is certainly one way to go.
yall take care now
John T
MarkB_MI
10-24-2007 18:07:44
The difference between 120 volt and 240 volt rated cables is the amount of insulation. Although the voltage to ground on a single leg of a 240 volt line is only 120V, there's 240 volts from leg-to-leg. If the extension cord gets hot, there's a much greater risk of an internal short with the lower rated cord.
Home Depot sells bulk 12/3 cable rated at 300 volts. I made up an extension cord for my compressor and it works great. However, for the distance you want to run, 12/3 is marginal. It takes a LOT of current to start a loaded compressor. If you're going to use the extension cord a lot, I think I'd go for 10/3. For occasional use, 12/3 will be fine.
jeffcat
10-24-2007 16:29:16
Take the easy trail. Go buy a couple of 50ft hoses. When i worked for Emglo we would see a motor now and then blow up cause of people not wanting to buy a couple of hoses. These machines all had comercial motors on them so it aint the motor bub. You can also use what is called a relay tank at the end of the line. Just tons of air at all times! Jeffcat
mud
10-24-2007 19:01:24
 Re: 12 ga. extension cords and 220 volts in reply to jeffcat, 10-24-2007 16:29:16
Best advice here tonight.
John T
10-24-2007 19:08:53
 Re: 12 ga. extension cords and 220 volts in reply to mud, 10-24-2007 19:01:24
Only minor drawback is you drop pressure across a long run of air line (depends on size and volume) same as you drop voltage across the long extension cord run..... ... However if air pressure drop across the line isnt too big of an issue and you use big air hoses/piping and I doubt hes running very high volume, it sure would be easy huh
John T
John T
10-24-2007 15:54:14
Tim, the issue is NOT so much if youre runnin 110 or 220 cuz the cords voltage rating is most likely rated welllll l above either. The issue is CURRENT and that 12 ga cord can safely carry 15 amps no problem (almost twice your 7 amps running load and well over 125% of the full sustained load)
You need 3 conductors, of course, the two hots and one safety equipment grounding conductor i.e. 12/3 or called 12/2 with ground.
The other issue is voltage drop but at only 7 amps load on 12 gauge conductors at 100 feet I dont forsee a problem but didnt run any calculations.
As far as how many watts of heat you dissipate over the entire cord, its I squared R but the R is fairly low on 12 gauge copper for 100 feet. Its also E x I (220 volts x 7 amps) so at twice the voltage and the same current it doubles, but the same motor only draws half as much current if the voltage doubles. BUTTTTT T the current rating of the cord is what the heat dissipation capacity is all about sooooo oooo if its rated 20 amps (depends on if in free air or conduit or whatever) then it can handle that current without exceeding the heat capacity of the insulation.
Have a plug n cord or other disconnect means at the motor of course and also of course current overload protection (proper sized breaker or fuze) back at the source to protect the feeders. The motor ought to have its own thermal overload to protect the motor itslef
John T Long retired n a bit rusty Electrical Engineer SO NO WARRANTY LOL
Stan in Oly, WA
10-24-2007 15:31:13
Hi Tim,
I entered "voltage drop calculator" on Google and got one that said that 12 gauge wire will carry 19 amps 100.4' with a maximum 3% voltage drop. When I entered 22.2 amps (7.4 X 3) it said that 12 gauge cannot carry 22.2 amps, not that it would carry it a shorter distance as I expected.
I'd be the world's biggest hypocrite if I cautioned you not to do something just because it was dangerous and foolhardy. Dangerous and Foolhardy is my middle name (actually it's Jameson.) I'm also sure that you're well aware of the potential insurance consequences you'd face if your insurance company ever heard you were doing something like that even in the same county where there was a fire. One thing I will mention though, is that you want to take a setup like that apart just as soon as you finish using it. Anything electrical that is jury rigged together is like a land mine waiting to blow up the next innocent person to touch it. Ask BuickandDeere his opinion of such a project if you want to encourage cursing that you will actually be able to hear all the way from central Canada.
All the best, Stan
supergrumpy
10-25-2007 07:30:08
 Re: 12 ga. extension cords and 220 volts in reply to Stan in Oly, WA, 10-24-2007 15:31:13
for some reason your response struck a chord
God protects fools, drunks and little boys. Only thing thats kept me alive.
Greg_Ky
10-24-2007 14:22:37
I doubt that the compressor will even start. Don"t forget to figure in that it will take around three times the running amps for starting. With that long of run and voltage drop I would be amazed if it started.
IH2444
10-24-2007 14:16:19
I think the current should be fine on a 12 ga cord 220 v 7.4 amps for 100 ft. The 110 volt connectors are another matter though. NEVER have a 220 volt outlet wired to a 110 volt receptacle. All kinds of bad things will likely happen.