Lots of folks here with strong electrical background from what I've read in the past. I'm in the process of wiring our new house which looks finished from the outside, but is totally open on the inside. I'm located in the rural with the closest neighbor about � mile up the road. No zoning or permitting as long as you own 10 acres or more and are doing what you do 200' from the nearest lot line. We have 15 acres and the 200' thing doesn't apply.
What I am planning on doing is wiring in an auxiliary electrical panel across from the main load center/panel. Went to Home Depot to get a sub-panel, but noticed that the 100-amp 12-position sub-panel cost $51 without any breakers. Right next door in the same aisle is a 100-amp 20-position load center/main panel with the 100-amp breaker and 6 20-amp breakers included for $60. These are both Square-D Homeline boxes. My logic tells me the 100-amp load center is the better deal money wise, safety wise, and roominess wise. Plan to gound this auxilaiary box with 2 5/8" ground rods and feed it with #2 copper in 2" PVC conduit (about a 35' run).
If anyone sees something here that may cause a problem with safety or something else, please reply.
dave guest
09-14-2007 21:07:22
 Re: OT-House Wiring in reply to Arkandan, 09-07-2007 04:10:23
PVC if in a burning building can give off poisonous toxic fumes according to insurance underwriter that I talked to. Master Electrician in MichigAN.
John T
09-10-2007 06:58:46
Dan, as noted below DO NOT RE BOND THE NEUTRAL (grounded conductor) AND GROUND BUSSES AGAIN AT THE SUB PANEL (if you go that route) .....
Unlike at the Main Service Entrance panel the Neutral and Ground busses are SEPERATE AND ISOLATED. At the sub panel the panels metal case is bonded to the Ground Buss but NOT the Neutral buss, its isolated.
Therefore, if you run wires from a main 120/240 Single Phase Three Wire panel to a sub panel you would use FOUR WIRES. Two Hots (Black n Red) One Neutral (white grounded conductor) one bare or green ground.
Usually the sub panel is lugs only no main breaker cuz the feeders are protected by the breaker in the main panel that feeds the sub panel
John T retired Electrical Engineer
Arkandan
09-10-2007 11:02:36
 Re: OT-House Wiring in reply to John T, 09-10-2007 06:58:46
Hi John, Good to hear from someone who has a presumed intimate knowledge of this subject(Electrical Engineer). I've got the panel mounted and have a pull rope in place ready to pull the wires through. I have done some reading on this site: Link Pretty informative. I have also reread some of my wiring books. I will have the "neutral" and the "ground" busses isolated in the "sub/auxilliary" panel. I'm still confused about grounding the "sub/auxilliary" panel "ground bus" to another ground rod. Would seem an added safety procedure to me, but sometimes what "seems logical or correct" is in fact not. What is your take on this, if you don't mind my asking? Thanks to all. Dan
John T
09-10-2007 13:15:13
 Re: OT-House Wiring in reply to Arkandan, 09-10-2007 11:02:36
Great question, heres the deal, its NOT so much an issue of any bonding of the safety equipment ground buss to Mother Earth, buttttt ttttt t, what IS IMPORTANT is that it be bonded (and only at main service entrance panel) to the Neutral buss so if a hot wire comes into contact say with a metal appliances case, the equipment grounding conductor is in place so it can carry fault current return (to trip the breaker n de energize the hot hazardous case) AND WHERE IS THAT CURRENT WANTING TO FLOW BACK TO????? THE NEUTRAL !!!!! NOT MOTHER EARTH. Its true that since the Neutral is mother earth bonded (driven rods n water pipes etc) and neutral is bonded to the panels equipment ground buss, theres voltage between the hot phase wire n ground buttttt tttt earth isnt as good a conductor as a copper wire and if a fault occurs (hot wire against drill case) you want a low impedance fault current return path so the breaker trips de energizing the hazardous hot drill case.
If the safety equipment ground buss was to mother earth ONLY and a hot wire got against the drills metal case, the earth is a high resistance path (depends on moisture n iron content etc etc) and a 20 amp breaker wouldnt trip buttttt tttt it only takes something like 50 milliamps through the old ticker to defibrilate it n you dieeeee eee cuz the breaker donT trip but the case is still hottttt
Out at the utility pole or pad mount transformer theres a transformer whose low voltage secondary winding has voltage between its 2 hot phases (240) and either phase and the center tapped Neutral (120). Current wants to flow via a conductor across/between those potential difference transformer terminals NOT from either to mother earth. The reason neutrals are tied to mother earth is so all have a common single zero voltage reference potential and earth is the best to use. The safety equipment ground buss and all those bare/green wires to an appliance metal case are there for fault current return so the breaker can trip and thats whyyyyy y its bonded to the Neutral at the panel cuz thats the place where current wants to flow NOT SO MUCH HIGH RESISTANCE EARTH.
Sooooo you carry seperate n isolated Neutrals (grounded conductor) n grounds (safety equipment grounding conductors) to the sub panels and DO NOT re bond them again (to prevent a situation where the right combinations of open neutrals n shorts may energize the ground buss circuit n you touch it n die) and theres no bonding of the equipment ground buss to mother earth cuz that dont do jack crap lol its the Neutral that gets bonded to mother earth at transformers n main panels for reasons above.
Hope this helps
PS just cuz Im an engineer dont necessarily mean I know know a dern thing more (probably less actually) then many other experienced electricians n others who answered, so go with their opinions also as Im long retired n very NEC rusty enginerr yet Im still knee deep in theory
John T
John T
09-10-2007 13:14:43
Hope this helps
John T
buickanddeere
09-08-2007 09:25:01
Just swap out the old small panel for a larger one. Why tinker around cobbling a 2nd panel together. You will not save any money or time.
dr.sportster
09-07-2007 12:57:29
I dont think its a NEC violation but it is highly unusual to use pvc conduit inside of a building.If its just the extra circuits you need place the two panels side by side and nipple between them.Dont even pipe across the room.If you must use e.m.t.[ISA LECTRSHUN}
Cliff (VA)
09-07-2007 08:10:24
Another option you might want to consider.
I have 350Amp service coming in at the meter (same price as 200A). The run is split at the meter box and goes inside to a 200 A load center and a sparate 200A stand alone main breaker. This load center feeds my basement and 1st floor. The stand alone breaker feeds another 200 Amp load center in the attic that serves the 2nd floor and attic.
Much more efficent when adding a new outlet in the attic.
There is a higher cost for the 400A meter box and the added cost for the stand alone breaker.
Something for you to consider,
Cliff (VA)
steveormary
09-07-2007 06:30:40
David-OR is right about the panel grounding.All nutuerals and grounds are bonded at the main panel. The grounding conductors(green or bare copper) are isolated from the grounded conductors(white) in the sub panel. If you have a friend who is a licensed electrician you may want to ask for his help.
steveormary
Ken Crisman
09-07-2007 06:14:26
The reason for the panel with only main lugs but places for individual breakers is that the subpanel will be controlled from a 2 pole breaker from the main panel . Using the other panel with main breaker is a waste of money due to having (2) double pole breakers in use . But that's your call as far as wasting money . Why are you using copper since its more money than aluminum ? You could use (3) #2 aluminum + (1) #4 aluminum for ground . Color code one of the #2 wires white for neutral at both ends & connect as neutral .Be sure to use the ground bonding screw in the main panel but eliminate the grounding bond screw in the sub panel since its not the main panel . You don't need the ground rods for the subpanel since you will be carrying the ground thru the #4 ground wire from the main panel . But the rods are needed for the main panel .Feed the sub panel with the appropriate double pole breaker . HTH ! God bless, Ken
Charles (in GA)
09-07-2007 13:07:18
 Re: OT-House Wiring in reply to Ken Crisman, 09-07-2007 06:14:26
For nine dollars more he gets a larger panel (more spaces and more room to work) and 6 circuit breakers worth $3 to $4 each. I wouldn't call this a waste of money.
Charles
Ken Crisman
09-07-2007 13:30:43
 Re: OT-House Wiring in reply to Charles (in GA), 09-07-2007 13:07:18
As I said , its his call . But it can be down by using the subpanel with main breaker or main lugs .God bless, Ken
David - OR
09-07-2007 05:39:43
Like Bill said -- unless the sub-panel is in a different building your thoughts of ground rods for the sub panel are all wrong.
You need to run a separate equipment grounding conductor (along with the hot and neutral wires) from the main panel to your sub-panel. It needs to be 8AWG copper or larger. You should NOT add any ground rods or tie the sub-panel to an external ground in any way (except through the equipment grounding conductor).
You need to isolate the ground from neutral at the sub-panel. Typically this involves removing a particular screw or screws that tie the panel case to the neutral bar, and adding a separate ground bar if one is not already there. The branch circuits that start at the subpanel need to have the neutral run to the neutral bar, and the ground run to the ground bar (unlike what you'll find in a typical main panel).
Your feeder (from the main to the sub) needs to be protected at the main panel by a suitable 2 pole breaker, regardless of any main breaker in the subpanel.
You can use the biggest, baddest panel you want for your sub-panel. The big-box pricing, as you've observed, has some interesting anomalies. A 200 amp, 42 circuit panel would be fine. Just make sure the connection lugs on the sub are listed for the size conductors you run -- sometimes a 100 amp feeder results in conductors too small to fit the lugs on a 200 amp panel.
PVC conduit, while allowed, is rarely suitable inside buildings. It isn't flexible enough to run through joists or studs, yet provides only questionable protection when run on the surface.
NM cable, SE cable, or flex conduit are better options for running through joists or studs. EMT is a better choice for running exposed. The 2 inch trade size you propose is needlessly large -- 1.5 inch or 1.25 inch appears to be adequate.
Building codes or not, you have a responsibility to future generations to make the wiring code compliant and safe. As I've gotten older, I've realized that none of us really "own" our possessions -- we just get to use them for a while until we die and the next guy takes them over.
glennster
09-07-2007 06:03:27
 Re: OT-House Wiring in reply to David - OR, 09-07-2007 05:39:43
Dave, what is the reasoning to not run seperate ground rods at sub panels? i"m not an expert on electricty by any means. it would seem on the surface that it would be a good idea. what are the dangers that creates?
John T
09-10-2007 07:13:43
 Re: OT-House Wiring in reply to glennster, 09-07-2007 06:03:27
Glenster, The NEC requires you to run SEPERATE grounds n neutrals to the sub panel and the Neutral and Ground busses ARE NOT BONDED BUT SEPERATE N ISOLATED AT THAT SUB PANEL.
Its possible to have the right/wrong combination of open conductors and/or shorts such that the equipment ground system (whats tied to metal cases of some tools n appliances) could become energized n shock n kill someone..... .
At the service entrance the Neutral (grounded conductor) is bonded to mother earth (zero potential reference) by made grounds such as driven into earth copper rods or other to earth grounds like metal water or gas pipes etc and the Neutral n Ground Busses are bonded together so the safety equipment ground buss (and its green or bare equipment grounding condustors) can serve as a low impedance current return path FOR FAULT CURRENT ONLY so the breaker will trip n save life and/or fires.
The earth grounding is for tying service Neutrals to a common zero potential earth grund reference while the bare/green safety equipment ground is for safety n fire prevention to provide a low impedance return current path to trip a circuit breaker in the event of a fault. Its for fault current ONLY while the Neutral (a grounded conductor) carries the normal non fault current to complete the circuit.
Hope this helps
paul
09-07-2007 22:20:05
Under very odd & difficult to believe could happen conditions, it sets up a loop in the same building which has power on that loop on wires that aren't supposed to show potential.
Only one ground spot per building.
If this were a seperate building, then never mind.
When I had my farm rewired, ran into an interesting deal. You are only allowed one power feed into a building. I had a building with 120v coming into a fuse box (ran one lightbulb & one plug). Same building housed the well controls, and had 240v into that corner. At the time of wiring back in the '70s this second feed was ok I guess, as it was dedicated to the well. Had to be re-mapped tho in this decade, one feed to the building.
--->Paul
Arkandan
09-07-2007 06:47:14
This is something I found on this site:>Link
[Quote]>Link "Why not connect the neutral and ground at other points in the system? Because if a neutral wire became disconnected (I've seen it happen), the return path for electric current could be along a ground wire. While that itself may not be a hazard, if that ground wire also became disconnected somewhere, parts of the ground system could be energized. That's not EVER supposed to happen.
The neutral wire is essentially a "low-risk" return path for the electric current in that branch of the system. All of the neutral wires all have the same electrical potential... nothing. At least, no potential compared to ground. There is, of course, 120 volts of potential difference between a neutral wire and any hot wire in the residential system.
If you touched the metal part of a live neutral wire you should not receive a shock. (But don't try it!) By tying the neutral to ground at one point, half of the conductors (in a typical 120 volt circuit) have no dangerous electrical potential. Of course, the hot wires are still dangerous." [End Quote]
From Ken: "Why are you using copper since its more money than aluminum ? "
I have some left over from a previous wiring project. 3 reels of approximately 75' each.
From David-OR: "Your feeder (from the main to the sub) needs to be protected at the main panel by a suitable 2 pole breaker, regardless of any main breaker in the subpanel."
Yup, noticed I didn't include that in my original after posting. Wish there was an edit feature on here. Putting a 70-amp breaker in the main to feed the "sub".
From David-OR: "Building codes or not, you have a responsibility to future generations to make the wiring code compliant and safe. As I've gotten older, I've realized that none of us really "own" our possessions -- we just get to use them for a while until we die and the next guy takes them over."
Well put and couldn't agree with you more. As long as I can afford it I usually will do overkill on any project I get involved with.
Still not sure why I wouldn't add the 2 ground rods to the new panel though. Sounds like extra protection to me. If I can do without them it would sure save a bunch of work and about $30. The rock to soil ratio here is about 50/50 at best. If anything the ratio would be tipped in favor of rock.
Lou NY
09-07-2007 10:30:20
 Re: OT-House Wiring in reply to Arkandan, 09-07-2007 06:47:14
The reason for not using seperate grounds on your system is to prevent ground loop currents, to seperate isolated ground can have a different potential which will result in voltage and current flow in the grounding system. It is usually low enough that a home or business would never notice it, however on a dairy farm, current and voltage on a ground loop can and will shock cows at times, micro-amps and milli-volts will effect cows. It is also noticable on industrial control systems and PC's at times.
In stoney ground we have laid ground rods lenght wise in ditches to aquire a good groung or ditch and wire to a wet location.
Luck
Lou
Arkandan
09-07-2007 12:45:16
 Re: OT-House Wiring in reply to Lou NY, 09-07-2007 10:30:20
I remeber that business with the stray voltage causing all sorts of problems for the dairy farmers in Wisconsin. I'm mpleased to report that there is no dairying on these premises. I did my tour there while growing up.
I am a little confused on your reasoning for not grounding the auxiliary/sub panel. It's my understanding that the new panel should have a seperate ground bar isolated from neutral. The ground bar will be tied back to the main panel via a #4 or #6 wire. I could understand there being a problem if one of the grounding connections were loose and not making good contact. If all were done properly then it would seem to me that I would have a much larger and better ground field. I am a believer in proper grounding after 35 years with GTE/Verizon. Also 4 years in the USN as an Electronics Tech. I'm not saying an electronics tech is an electrician, but I do have a working knowledge of electricty and it's eccentricities. I am always willing to learn though and thanks to all the repliers.
Bus Driver
09-07-2007 06:52:41
Adding the ground rods is fine. But code provisions must be followed regarding the equipment grounding conductor for the main service panel to the subpanel. Having a main breaker in the subpanel is perfectly OK and as I read your post, is the lower-cost choice.
suptscottyb
09-07-2007 05:38:15
The question of grounding sub panels seems to something that comes up every couple of years.
I"ve gotten different opinions from the same inspectors at different times. I"ve got 3 subpanels at the ranch and all have their own ground rods. Of course they are also tied together with the neutrals. What does the National Electric code say now?
Bill in IN
09-07-2007 04:43:07
I wouldn"t advise grounding your sub-panel seperately. It would be a code violation that your insurance company wouldn"t approve of, and coul lead to some real interesting effects in your house.
I wouldn"t use PVC conduit either. THW/THWN in EMT or NM cable.
Not knowing the numbers of the panelboard/load center it would be hard to say- but if one is a panelboard it is a much higher grade piece of equipment than a load center. There isn"t anything wrong with a loadcenter, has to do with AIC ratings, layout etc. Probably both are load centers as I don"t know of any Homeline that isn"t.