Tool Talk Discussion Forum
Basic Wiring?
dhermesc
06-14-2007 07:56:01
I have been wiring my basement and recently hit a snag.
I ran a 3-12 wire into the breaker box; I grounded the white wire and the "bare" copper wire and connected the red and black to their individual 15 amp breaker switches (I know I don�t need 12 guage on 15 amp but I have a large supply 12 guage wire). Flipped the switches and one works fine but the other (red) blows when flipped.
Thinking I had a problem down stream I pulled the covers off all my junction boxes, outlets and light switches but found nothing obvious.
My next step was to unhook the red wire at the first junction box down stream from the breaker panel thinking I would look for it by steps � capped it with the connector but the breaker switch blew when flipped. I thought I had a bad breaker switch so I replace the original with another it blew again upon being switched. Any idea whats up?
suptscottyb
06-19-2007 13:24:52
 Re: Basic Wiring? in reply to dhermesc, 06-14-2007 07:56:01
I read all of this. The one thing I hear again and again is what a bad time you had snaking the wire into the panel. That's where I would look for a short - romex isn't very tough. I've damaged it pulling around a corner - panel edges can be sharp.
Jack-Illinois
06-16-2007 20:03:05
Your last statement is the answer - the red wire is shorted to the bare (ground) or to the white (neutral) at or before the first junction box.
Also to prove the rest of your red circuit is good, while it is broken at the first junction box, hook the outgoing red wire to the black circuit in that box and this should give you 120v on all the devices on both the black and red circuits. This will prove that your problem has to be at or before the first junction box. If it makes the black breaker trip then you have double trouble.
Jim K
06-16-2007 19:13:38
One little trick that I use to help find hard to find short circuits, is to makeup a 1' piece of extension cord with a female cord end on it.
And on the other end I strip 6" of the outer jacket of the cord and strip off an appropriate amount of insulation on the white wire and the black wire. Now I plug it into a droplight {incandescent) and then I'll wire it in series with the offending circuit right at the panel.
Now you can walk around with the light and check for shorts (take apart connectors and wiggle wires)as soon as the bulb goes out or flickers you found the short and the breaker won't constantly be tripping.
Good luck
P.S. use a connector at all junctions and all junctions shall be made in junction boxes w/covers. I've had to straighten out some messed up owner done wireing. It's ammazing what people will do unknowingly putting thier lives and thier families lives in danger.
Jim K
buickanddeere
06-16-2007 22:09:40
 Re: Basic Wiring? in reply to Jim K, 06-16-2007 19:13:38
I agree, call in a pro. Why play with fire where you and your family sleep?
seabee01
06-14-2007 16:27:34
sounds like an L16 has been tightend too much, been there done that..lol, check connectors, you will see where it is bad.
cj3b_jeep
06-14-2007 13:49:17
In my neck of the woods, the electrical inspector would fail 12 wire on a 15 amp circuit
jokers
06-17-2007 07:37:19
 Re: Basic Wiring? in reply to cj3b_jeep, 06-14-2007 13:49:17
If that is true it wouldn`t hold up under appeal. To prevent excessive line loss(voltage) over long distances, conductor size must increase for a given circuit and 12 gauge wire with a 15 amp breaker is common.
I`m going way back in my memory but I seem to recall that to keep line loss at or below 2% in a circuit, the circuit must be no more 70 feet long. Alot of "home run" circuits in the modern large houses being built are at or very near this distance so a larger conductor is used in the run to the breaker.
buickanddeere
06-14-2007 18:25:24
Other way around. the hydro inspector would rightfully throw a fit in ost cases where #14 wire is sued with a 20amp breaker. Motor loads with thermal and overload protection excepted.
Stan in Oly, WA
06-14-2007 15:44:06
Hi cj3b_jeep,
And the aggravating thing is you never seem to have a big, long sock full of horse manure to smack them with when they really, really deserve it.
All the best, Stan
cj3b_jeep
06-14-2007 16:02:17
 Re: Basic Wiring? in reply to Stan in Oly, WA, 06-14-2007 15:44:06
When we were building our house 3-4 years ago my wife wanted to go out in the woods behind the house and dig a bunch of shallow graves for them. Just went through it again with my 24x32 pole building.
dhermec
06-14-2007 14:29:49
Why?
cj3b_jeep
06-14-2007 15:17:59
 Re: Basic Wiring? in reply to dhermec, 06-14-2007 14:29:49
Does not me sense to me either, as the breaker will be the part taking the load, then you have the option of making it a 20 amp circuit later by changing the breaker and outlets, but around here, the inspectors seem to make up their own rules.
buickanddeere
06-14-2007 10:45:28
A couple of things. The bare/ground wire goes to the ground bar which has a direct connection the the hydro services ground rods. If there isn't at least two 10 ft rods driven at least 10 feet apart and connected to the service with #6 copper.Install them The neutral is a separate wire and function. It's not an insulated and colour coded current carrying conductor for nothing. You didn't split your split receptacle. There is a metal link to break out between the two brass screws, one screw holding the black & the other screw holding the red. You did connect the white to the shinny screw and the bare to the green screw?
buickanddeere
06-14-2007 10:53:24
  Re: Basic Wiring? in reply to buickanddeere, 06-14-2007 10:45:28
Quote "Flipped the switches and one works fine but the other (red) blows when flipped. I replace the original with another it blew again upon being switched" Unquote. You mean you are not using a two pole breaker to supply the split receptacle? That's an accident waiting to happen. b.t.w. even the other breaker that appears ok when the other "blew". No manufacture will warranty or guarantee protection after a breaker has tripped on fault current. The trip value scan and will change after interrupting a fault. This is the kind of situation where tradesmen cringe when working on Mr. Tinkers home repair/installation. I know it costs, but it�s better to hire a pro. Your home fire insurance won�t be canceled should claim arise either. Insurance companies will weasel out any way they can.
dhermesc
06-14-2007 11:45:41
 Re: Re: Basic Wiring? in reply to buickanddeere, 06-14-2007 10:53:24
I am not hooking into a split receptacle.
One hot with a common ground/neutral will supply some of the outlets in the basement the second hot and common neutral/ground will supply power other outlets.
I am using a 3-12 wire because I'm running out of room to snake the wires into the breaker box.
buickanddeere
06-14-2007 11:58:15
 Re: Re: Basic Wiring? in reply to dhermesc, 06-14-2007 11:45:41
Then there must be pierced insulation on the red Line 2 likely at the breaker box's L16 connector, the L16 in the 1st junction box or a staple through the cable. When you say "Common ground & neutral"? This cable does have a bare, insulated white, insulated black and an insulated red? Is there any place at all where the white and bare are connected together?
dhermesc
06-14-2007 12:27:45
 Re: Re: Basic Wiring? in reply to buickanddeere, 06-14-2007 11:58:15
Could you explain "L16"
There are no staples "through" the wire. All electrical staples (plastic 1/2 inch with two nails) are definately properly installed.
Yes.
No.
buickanddeere
06-14-2007 12:56:04
 Re: Re: Basic Wiring? in reply to dhermesc, 06-14-2007 12:27:45
L16, L17 etc are the trade names for a box connector. The L17 is larger than a L16. They have a threaded body that is fastened through the electrical box's knock-out with a lock-nut. There is a clamp on it's main body that is tightened with a screwdriver in order to hold the cable. It's not unheard of to over tighten the clamp and pinch a conductor's insulation.
dhermesc
06-14-2007 13:17:44
 Re: Re: Basic Wiring? in reply to buickanddeere, 06-14-2007 12:56:04
"It's not unheard of to over tighten the clamp and pinch a conductor's insulation."
That's possible (used a cordless drill) at the junction box - no clamp at the breaker box.
paul
06-14-2007 20:15:27
 Re: Re: Basic Wiring? in reply to dhermesc, 06-14-2007 13:17:44
That might make the pro's cringe a bit. I'll attach the boxes to the wall with a drill, but a much better feel for things if you use a real screwdriver with an elbow-power for the wires themselves. Kinda easy to spin things over with a drill & not even know it.
--->Paul
buickanddeere
06-14-2007 14:45:09
There has to be a box connector at every box, junction etc. This might be a good time to call in a pro before sparks, fire or injury/death.
Stan in Oly, WA
06-14-2007 10:37:26
Hi dhermesc,
Post your findings when you get this solved, would you? I'm always interested in this kind of mystery.
All the best, Stan
huntingreen
06-14-2007 10:24:35
On a multiwire circuit make sure you wire nut the white wires together with a pig tail to the receptacles. You dont to connect the in white and out white to the receptacle.
dhermesc
06-14-2007 11:47:16
 Re: Basic Wiring? in reply to huntingreen, 06-14-2007 10:24:35
In the case the "pigtail" is what runs to the outlets, I'm not daisy chainng the outlets.
buickanddeere
06-14-2007 18:29:08
 Re: Basic Wiring? in reply to dhermesc, 06-14-2007 11:47:16
Hunting Green did raise a very important point. The grounds have to be marreted together too. Now this is a good way to start an argument but..... . The manufactures of wirenut and wingnut state that if the proper sized nut is used with the proper size and number of conductors. There is no reason to then goober up the joint with tape.
John T
06-14-2007 10:11:17
DH, if that circuit breaker trips soon as you flip it on, the red wire connected to it must be shorted (to bare Ground or white Neutral) somewhere assuming the breaker is okay.
I take it you have 12/3 with ground (total 4 conductors) from your post correct?????
White wires to panels Neutral Buss Bare grounding conductor wires to panels Equipment Ground Buss Red and Black hot phase conductors to breakers
If she dont trip with the red wire removed from the breaker, theres must be a short instead of a breaker problem..... ..... .
Using that 12/3 with ground having red and black phase conductors sounds like you may be running whats called a multi wire branch circuit
CAUTION !!!!! !!!!! !!!!! !!!!! ! if youre doing that, the breakers should be tied (or use a 2 pole circuit breaker) so if one hot leg trips out the other leg is also de energized. Someone could throw the one breaker (say the black) and go into a junction or outlet box thinkig the breaker was offfff fff buttttt ttttt that other red wire IS STILLLLL HOTTTTT TTTTT T
Ive designed and specified multi wire branch circuits (2 hots using a common single neutral) which can save copper from running two neutrals buttttt tttt the breakers were tied or I used a 2 pole breaker buttttt tt Im NOT a fan of them for safety considerations plus they arent suitable for inductive loads like transformers or power supplies or light ballast circuits and would advise one to avoid them unless they use all design and wiring safety precautions.
If thats (multiwire) not what you meant disregard all this excepot for finding that short
John T, Long retired and NEC rusty Electrical Engineer
dhermesc
06-14-2007 11:56:07
 Re: Basic Wiring? in reply to John T, 06-14-2007 10:11:17
"Ive designed and specified multi wire branch circuits (2 hots using a common single neutral) which can save copper from running two neutrals"
This is what I've done. I wasn't hoping to save on copper so much as its a real B**** to snake the wires into the breaker box. I was hoping to run my basement outlets on two circuts (the one causing all the questions), lights on a third and a bathroom on its own GFI circuit.
Have I screwed up by not using a two pole circut breaker in his application?
Charles (in GA)
06-14-2007 18:56:23
 Re: Basic Wiring? in reply to dhermesc, 06-14-2007 11:56:07
You must use a two pole breaker, or at least, the red and black must be powered by opposite sides of the busses in the breaker panel (a two pole breaker will do this for you) otherwise you can overload the neutral.
Charles
Charles (in GA)
06-14-2007 18:56:11
Charles
John T
06-14-2007 13:04:26
Im just saying ANYTIME I specified or used a multi wire branch circuit I used a 2 pole breaker so in case one was triped they BOTH were. That way could prevent an injury from one who was unaware there was still a hot live wire present even though one of the breakers was shut off. If they are BOTH off that hazard is eliminated.
best wishes n proceed with care John T
Charles (in GA)
06-14-2007 20:02:55
 Re: Basic Wiring? in reply to John T, 06-14-2007 13:04:26
I wholeheartedly agree. But the last time (on another board) that I stated that you had to have a tied handle double pole breaker on multiwire, I got chastized by an electrictian because the code didn't require it in ALL cases. Better safe than sorry.
Charles
John T
06-15-2007 06:23:07
 Re: Basic Wiring? in reply to Charles (in GA), 06-14-2007 20:02:55
RIGHT ON CHARLES, I AGREE, Theres no way I would use two individual untied breakers for the reasons I stated above SAFETY AND LIFE SAVING. The NEC is a minimum requirement while it never hurts to be over safe and design beyond it.
John T Long retired electrical engineer but still safety conscious
neblinc
06-14-2007 08:18:11
I had a dead short in the very last circuit of my shop. I double checked everything and could find nothing wrong. Traced it down between 2 outlets, took the steel siding off the outside since it was drywalled and found 1 of the clamps on the metal box had punctured the wire.
Randy
Gary from Muleshoe
06-14-2007 08:11:45
It is obvious that you have a dead short. Step #1 With an amp meter set to ohms. Disconnect wire from beaker. Black lead to ground bar in breaker box, red to red wire if meter pegs out you have a short. Step #2 Disconnect the white wire. Black lead to white, red to red, if meter pegs these to wires are making contact some where down the line. Start by checking every connection you made down the line. At every connection disconnect both wires and repeat step two. Also if wire is run through conduit, you may have scraped insulation off when pulling through. Good luck.
dhermesc
06-14-2007 08:24:43
 Re: Basic Wiring? in reply to Gary from Muleshoe, 06-14-2007 08:11:45
"by checking every connection you made down the line. At every connection disconnect both wires and repeat step two."
At this stage there are no connections down the line - I unhooked the red wire at the first junction box (about 14 feet from the breaker box) and capped it (left the common ground hooked up)- that�s why I thought I had a bad breaker.
I will start with disconnecting the wire from the breaker and checking the breaker in the box - if it shows a short there how lucky am I that haven't electrocuted myself?
old art
06-14-2007 15:05:59
 Re: Basic Wiring? in reply to dhermesc, 06-14-2007 08:24:43
are these wire in a conduit or is it romex
if it is romex the wire is damaged inside of the covering between the breaker panel and the first junckion point.remove it and start again. look at what you take out you will find it is damaged.