Tool Talk Discussion Forum
Emergency generator
BobReeves
01-12-2007 14:03:44
We have a big time ice storm on the way and the news is going crazy with warnings.. Thought I would beat the rush and go buy a generator just in case. Ended up I didn't beat the rush by very much, only thing I could find was a Troy-Built 5550 watt job at Lowes. Ended up getting one of the last ones they had.
Anyway I have it home and in the shop getting ready to unpack it. We live in a mobile home and I did all of the electrical work when we moved it to our property.. Inspector signed off on my work so must have done something right.. Guess what I am trying to say is I won't have any trouble hooking the generator up and disconnecting the house from the grid if it's needed during this storm but I would like to get some sort of manual transfer switch for possible future emergencies.
Any hints on the generator, transfer switch etc. would be apreciated...
BobReeves
01-13-2007 09:59:24
 Re: Emergency generator in reply to BobReeves, 01-12-2007 14:03:44
Ice took down my internet connection for a while and am just now getting back on-line. Wireless is great when it works...
OK you sold me I will get the proper transfer switch when I get a chance and do it properly. However I can"t get out my drive and I"m telling ya if we loose power I am going to get that puppy hooked up one way or another...
On the neutral backfeed issue... I still don"t believe one wire that is tied to earth ground can in any way back feed anything to the grid, transformer or not.. You would need to have something going into at least one of the legs to complete a circuit and if they are both disconnected how can anything be back fed. I do know how transformers work even designed a few and no way can you get anything out with only one wire hooked up... Please explain under what circumstances leaving the neutral connected can create a back feed?
buickanddeere
01-13-2007 22:19:02
 Re: Emergency generator in reply to BobReeves, 01-13-2007 09:59:24
Link
Due to voltage drop on causing a diffference in potential. You have to look at page 2 for a while to see it.
BobReeves
01-14-2007 14:29:53
 Re: Emergency generator in reply to buickanddeere, 01-13-2007 22:19:02
Checked out the diagrams, looks to me like in two of the samples they don't switch the neutral.. My generator has separate ground and neutral connections that are not electrically tied together, looks like if I don't tie the neutral to ground I won't need to switch it. Also the lockout pointed to by Crem below can't switch the neutral and it's suppose to be approved by all kinds of laboratories.
Still don't see how the neutral can back feed. In order to create any voltage in the transformer more than one wire would need to be hooked up. You can put 600 volts on one wire of lets say the primary a transformer and unless you provide a return with the other end of the (primary) winding you aint gonna get nuttun out of the secondary.
I can understand the possibility of a voltage difference in potential between neutral and ground.. Maybe induced current could create a couple volts... But if the natural and ground are tied together at the transformer??? Even if you end up with a difference between N & G you still don't have a complete path (return) through the line transformer..
Bet this is one of those regulations that was written as the result of someone doing something really stupid.
In any case it looks like we dogged the bullet, storm has all but passed and we still have power.
CNKS
01-12-2007 18:51:27
Put your generator outside your house, run extension cords from the generator outlets to electric space heaters, refrigerator, etc. Then get an electrician to wire the generator into your breaker panel, or do it yourself PROVIDED you get it inspected. I have lot of respect for the people on this forum, but electricity, particularly when there is a very real possibility that it will backfeed and kill someone, is not something to mess with. Also, if you intend to run everything in your trailer, (depending on what you have) with a 5500 watt generator, you can't, particularly considering the surge (startup requirement) of your refrigerator, furnance, etc, so just use the essential items. It is an emergency generator, not a substitute for the real thing.
dave guest
01-12-2007 18:17:03
Bout 10 years ago in Mich, at a trades meeting of Union Electricians, we were told by Edison rep that they send people out during power outages, looking for lights on in house. If you are caught with a generator improperly hooked up, at that time, Edison said you would have your service disconnected for a very, very long time. Please use proper wiring. Would you like to explain to a lineman's family why you caused his death?
Crem
01-12-2007 18:05:01
I came across this interlock kit awhile back but don't know much about it. Maybe someone will comment on it.
BobReeves
01-14-2007 13:10:05
 Re: Emergency generator in reply to Crem, 01-12-2007 18:05:01
Wow, $150.00 for a couple pieces of sheet metal.. Good idea and worth stealing :)
buickanddeere
01-12-2007 19:02:48
Ok if the generator floats the neutral instead of bonding it.
the Unforgiven
01-12-2007 16:53:34
 Re: Emergency generator Central NE in reply to BobReeves, 01-12-2007 14:03:44
Hi Bob, I have been running a 5000 watt Coleman for the last two weeks, most of it on lp. I have a big disconnect on my pole with an aux. power-disconnect switch built in. I was not prepared to use it, and I am now wired in to a 60 amp breaker in my garage. I wired several up last week, some into A/C disconnects, some breaker panels and some into meter sockets if there was no real disconnects. Some guys have a double male cord and plug into the dryer or stove outlet, works pretty clean and pretty universal. I ran out and bought a couple generators when I saw the first poles break so I beat the rush, but just barely. Just one of the big hardware stores sold 400 generators the next day concert ticket style, and I heard 1500 the next day. Well guess what, every body gets home and figures out that they need a cord, and all of a sudden you can't find a 30amp plug within a hundred miles. A lot of people are back on, I have at least one and one-half miles of lines down between me and commercial power, and no crews in the neighborhood yet.
railhead
01-13-2007 06:24:28
 Re: Emergency generator Central NE in reply to the Unforgiven, 01-12-2007 16:53:34
Unforgiven, Just a thought, if you have a coleman with the coleman (no name chinese engine), shut it down daily and change the oil. We used them on the railroad to run crossing gates during a storm and they ran 2-3 days before locking tight. we guessed the block is just made from pot metal junk. Use synthetic and you may be able to run it longer.
Hope you get power back soon. I was ready but the ice hit here acutally South of us and looks like all we will get now is a lot of sleet. (NW Oklahoma).
the Unforgiven
01-13-2007 13:50:44
 Re: Emergency generator Central NE in reply to railhead, 01-13-2007 06:24:28
Hey rail, it is an ohv Briggs 9hp, looks like a Honda copy, made in Japan. Since I switched to lp I have been running 24/7, changing oil at 80-90 hours, and the oil looks so good that I am tempted to pour it in my 350 Chevy beater. I bought another with a 10hp Tecumsuck the same day to use as a temp to warm up other houses and as a back-up, the generator part started acting up at about 50hrs, took it back to the factory for repair since they are only 40 miles away, and it ran another 6 hours and blew all the oil out of the main seal on the pto side. I just returned from cashing it in for a replacement. I really like the Briggs Vangaurd so far, after a 24 hour run the crankcase is cool enough that you can hold your hand against it.
buickanddeere
01-13-2007 14:25:21
 Re: Emergency generator Central NE in reply to the Unforgiven, 01-13-2007 13:50:44
That overhead valve Briggs that looks like a Honda maybe a Generac Engine. A good thing for you if it is. Does it have an oil filter? The Generac/Guardian generator line is the best value per $$$ of anything on the market.
Not me
01-12-2007 16:37:18
I made up a double male cable to backfeed my dryer receptacle. I have two seperate disco's and i open both.
Johnski
01-12-2007 15:58:52
Uncle
01-12-2007 14:25:11
I know it"s not right by any means but I use a spare breaker and backfeed the house.
I disconnect the Main Disconnect, Dropp the 220 circuits and then fire up the generator and back feed through a 60a breaker.
The utility Comp. will ground out their line to protect the workers, so make sure you disconnect the mains or you"ll fry your gen.
BobReeves
01-12-2007 14:45:56
 Re: Emergency generator in reply to Uncle, 01-12-2007 14:25:11
Not a bad idea, have a 200 amp distribution panel that feeds the house and shop. Would be fairly easy to add another breaker tied to a 220 plug and make up a jumper cable.
Could trip the shop breaker to disconnect it and the main to disconnect the whole works from the grid.
BobReeves
01-12-2007 15:57:32
 Re: Emergency generator in reply to BobReeves, 01-12-2007 14:45:56
Not saying you are not correct in fact I agree with what you are saying but sometimes Oklahoma engineering is necessary in a pinch :)
The distribution panel is outside on a short pole right next to the line transformer. Am almost sure the neutral is tied to a ground rod at the transformer. Transformer is fed from an underground cable from the pole out on the road. I can't see how the neutral could possibly carry anything back to the grid..
buickanddeere
01-12-2007 16:43:53
 Re: Emergency generator in reply to BobReeves, 01-12-2007 15:57:32
Bob
A little knowledge is a dangerous thing.You wired your house but are not sure why it passed? A neutral will backfeed voltage as it raises above true earth due to voltage drop. 2V on the secondary side is over 200V on the primary side of the service transformer. That's enough to injure or kill. Why do you think a bonded generator needs a three pole switch and a floating generator requires a two pole switch. It's to prevent neutral-ground loop circuits. As for those home tinkerers who know more than the hydro inspector and electricans. Wonder on down to the Wiremens Union Hall and tell them you don't need transfer switch for your generator.And backfeeding with a double male cable while counting on the main for isolation. Make certain your health and life insurance is paid up before telling these guys. Cheepskate backfeeders are ignorant low life scum.
the Unforgiven
01-12-2007 17:06:52
 Re: Emergency generator in reply to buickanddeere, 01-12-2007 16:43:53
So even if you pull the meter out you can still backfeed through the nuetral?
buickanddeere
01-12-2007 19:00:19
 Re: Emergency generator in reply to the Unforgiven, 01-12-2007 17:06:52
Yes. Purchase a Ronk Meter Base transfer switch. 2 Pole if the generator floats and 3 Pole if bonded.
Gerald J.
01-12-2007 15:38:46
If you install a mechanical interlock so that the main and generator breakers can't be on at the same time, the NEC accepts that as an alternative to a separate switch.
Gerald J.
Mattlt
01-12-2007 15:38:26
No, no, no. Even with the main breaker turned off, you're still backfeeding over the neutral. This could fry a lineman.
Not to mention the "double male" jumper cable you're talking about. Not good having an exposed (hot) male end.
Get the proper transfer switch. Do it right.
Gerald J.
01-12-2007 17:05:43
 Re: Emergency generator in reply to Mattlt, 01-12-2007 15:38:26
First, I DO NOT ADVOCATE THE DOUBLE MALE CORD. That's a killer device.
Second that ground current from the high line comes from the power system being grounded and the fact that a significant portion of the return current passes through the LARGE cross section of the earth, no matter how large the power line's grounded conductor. Unless there is a ground fault in the generator, most generators aren't grounded at all so there is no ground and it won't be transformed back to the power line. That voltage is the resistive drop from that primary current fraction into the ground. Its a MUTUAL voltage, not a transformed voltage.
The Square D switch I have out on my pole at home does NOT break the ground or neutral, only the phases. The interlocked square D breakers I have in my barn don't either and the interlock was in place when the untility crew wired the meter and the service into that panel. They agreed it was good.
Gerald J. Electrical Engineer in Iowa.
Dan hill
01-13-2007 02:33:20
 Re: Emergency generator in reply to Gerald J., 01-12-2007 17:05:43
An oil furnace can have a plug in its power feed so you can run it with a good extention cord.This isolates the generator.Freezers and refrigerators can be powered the same way.Watch out for carbon monoxide.Has there been any solid info on feedback.All lineman work on lines as they are hot at all times.My Dad spent most his years working for electric company.
buickanddeere
01-12-2007 19:27:22
The ground is never ever switched or opened for any reason. The ground is never to be a current carrying conductor except during faults. The ground is used to hold the neutral of the utility transformer down to earth potential for safety. The neutral requires switching, therefore a three pole transfer switch. If the generator has the neutral and ground/chassis bonded together. Which should be the case with small portable generators with U-Ground and Twist-Loc receptacles. If the generator's neutral floats isolated from ground/chassis, then a two pole transfer switch is required. >Link
>Link Electric Technician, IBEW Interprovincal Electrician with CFFF endorsement and Nuclear Control Tech with OPG.
ric1
01-12-2007 16:51:20
i just had a new electric box installed it has a breaker that one way is for the generator and the other direc tion is for main electric service it can only be one or the other.
buickanddeere
01-13-2007 14:27:10
 Re: Emergency generator in reply to ric1, 01-12-2007 16:51:20
You are wiser than the average person by far.