It got a little long and cornfusing below, I thought it best to start a new thread to answer the original posters last question, cuz its very critical concerning his safety and understanding: ORIGINAL POSTER LAST QUESTION: Thank you for an excellent and easy-to-understand explanation of white versus green/bare. My question is, from the main to the sub panel, can you just run the 220 volt black/red/white (3 wires = 2 hot, one neutral) and then install a new ground rod for the sub panel to replace the green/bare? REPLY: The answer is NOOOOO OOOOO OOOOO OOOOO OOOOO O. If you drove a rod into mother earth at that sub panel VERSUS running the 4th bare/green equipment grounding conductor from the main panel YOU DO NOT HAVE A DIRECT LOW IMPEDANCE CURRENT PATH BACK TO THE MAIN PANEL TO TRIP A CIRCUIT BREAKER AND CLEAR A POTENTIALLY HAZARDOUS FAULT. Mother earth, depending on the moisture and mineral content and the grounding electrode quality, is NOT a good low impedance current path, therefore if say a steel cased grounded electric drill (that uses the 3 wire grounding plug) got shorted to a hot live phase wire and since that ground rod you drove is a high impedance path back to the panel, if you touched the case and were standing on moist earth or another good current path back to the panel, YOU COULD DIEEEEE E. You see the electricity is seeking a current path back to the service transformer (thats where the voltage difference is) and earth isnt a good path. However, if you run that 4th equipment grounding conductor from the main to sub panel (as we told you), it IS A GOOD LOW IMPEDANCE CURRENT RETURN PATH back to the transformer (to trip a circuit breaker to save your life) via the Neutral and Ground busses being tied at the main panel which is served by the transformer. The reason the Neutral, at BOTH the pole or pad mount transformer, PLUS at the service entrance is tied to a grounding electrode (driven rods or water or gas pipes) to Mother Earth is to bring everything back down to a common zero reference. That driven ground rod you wanted to use simply DOES NOT suffice as a good return current path back to the panel to trip a circuit breaker to clear a dangerous fault. RUN 4 WIRES TO THE SUB PANEL FOR 120/240 VOLT SINGLE PHASE 3 WIRE SERIVICE 2 Hots,,,,, ,1 White Neutral (a grouned conductor),,,,, 1 bare/Green Equipment Grounding Conductor. RUN 3 WIRES TO A 120 VOLT LOAD 1 Hot, 1 Neutral, 1 Equipment Grounding Conductor. Hope this helps John T retired electrical engineer