glennster
12-06-2006 12:02:14
Re: Electric circuit testers troubleshooting in reply to BobOHIO, 12-06-2006 06:44:57
go to your home center, pick up a tester called a wiggy. has two wires, reads voltage and also will rattle when you have power. go to your main panel, remove cover to expose innards. be careful, at this point all the circuits are exposed, if you lost the neutral, and you complete a circut with your hands ect.....it will be bad. you should have 3 cables coming in the service panel, usually at the top. 2 of them should be 110 volt hots, the 3rd the neutral. the two hots will go into the bank of breakers or fuses. the 3rd will connect to the neutral buss, you may have a 4th wire to the ground buss too if it is a newer box. put the wiggy probes on the two 110v hots, the wiggy should read 220volts. if you dont get power here, you have a problem from the box to the meter. next put one probe on one of the 110v hots and the other to the neutral bar. you should get 110v here. do the other hot the same way. if no reading test from each hot and putthe other probe on the neutral wire itself, not the buss. this will show if the neutral is lost at the buss connection. if you are showng power at all these tests, your main breaker is probably blown, trip it and reset the main breaker, if it is the fuse type, it will have cartridge fuses, 60 amp, 100 amp, ect, replace the cartride fuses. if you still have no power, call a licensed electrician in, because its probably a serious condition, and you could injure or kill yourself quik