A 300 foot one-way run is pretty far to carry 100 amps. At this distance it is worth considering a second meter. Have an ambulance on call when you price out 900 feet of 2/0 copper. Copper of all sorts has gone up 5x in price in the last couple of years. Lots of Chinese families can now afford washing machines and the worldwide demand for copper has skyrocketed. As much as I hate aluminum wire, economics will likely push you in that direction. The neutral conductor can be smaller than the hot conductors, as can the ground conductor if you provide one. The 5% total voltage drop budget in the NEC is a "fine point note", not a code requirement. It does not have regulatory force, per se. Depending on what you are going to do out there, you could consider sizing the feeder smaller than would otherwise be required for a 2% or 3% voltage drop. If one of your big reasons for a 100 amp subpanel is a stick welder, and you don't mind the lights dimming as you strike an arc, you may be able to size the wiring to what is required for ampacity rather than voltage drop. But if the job is to be inspected, run this thinking past the inspector. Some of them may choose to enforce the voltage drop because they (incorrectly) believe it to be code, others may invoke the "neat and workmanlike manner" clause just because they think that's how the job should be done.