Lenray, It depends on just what service you want for each of the RV hook ups. Many standard RV receptacle stations have one 120 volt 30 amp receptacle (for most standard 30 amp 3 prong RV plugs) plus another 120 volt standard 15 amp 120 volt duplex NEMA 5-15R convenience receptacle which is on the opposite phase from the 30 amp outlet next to it. The larger RV's have a 120/240 volt 50 amp 4 prong receptacle so they can run 2 AC's at once, so if you want such a receptacle at each of the three RV stations we gotta refigure. My guess is you probably just need three standard 30 amp RV receptacle stations which have the one 120 volt 30 amp 3 prong RV receptacle plus a standard 120 volt 15 amp duplex convenience receptacle next to it. OF COURSE, you could get by without the standard duplex convenience receptacle i.e. just have a 30 amp 120 volt 3 prong RV receptacle for each of the RV's cuz many have their own external 120 volt 15 amp weatherproof convenience outlet somewhere on the side. HOWEVER a standard 30 amp 3 prong 120 volt RV receptacle is the minimum I would place at each of the three stations..... Nowwwww for the service it appears you need a standard 120/240 volt single phase three wire 100 amp minimum. A Typical installation would be a rigid conduit riser up through the roof or on the side of a building with a weatherhead on top where your 3 service entrance conductors (2 Hots and one Neutral) splice to the utilitys service and then run down into your service entrance panelboard. The utility likely wont hook up to your service till its been inspected and approved and either at the meter base or the service entrance panel the Neutral must be bonded to a proper grounding electrode such as a driven earth ground rod etc. Your main panel must be a 100 amp minimum 120/240 volt with a 100 amp 2 pole main breaker suitable for service entrance and space for maybe 12 to 20 breakers breakers allowing room for expansion. It will have a Neutral plus an Equipment Ground Buss which is bonded together (plus metal case of panel is also bonded to the equipment ground buss) as its the service entrance. Then you would install at least the three 30 amp single pole 120 volt breakers to serve the three 30 amp RV receptacles, I would feed two on Phase A and the other on Phase B using 10 gauge wire with 3 conductors (Black Hot, White Neutral, Green Ground) to each RV station. Then if you go with another 15 amp 120 volt duplex receptacle at each station I would serve them with three more 20 amp single pole breakers and run 12 gauge 3 conductor wire to them. Summary, you need at least a 100 amp 120/240 volt single phase three wire service (could run a 200 amp service if you want expansion and other use there) and a service entrance suitable panel with a 100 amp 2 pole main breaker and room for at least 12 breakers. Run 3 10 gauge wires to the 30 amp RV outlets and 3 12 gauge wires to the 120 volt NEMA 15R convenience duplex receptacles. Normally the riser and weatherhead would run to a meter base with conduit and three wires rated for 100 amps and then from the meter base into your service entrance panelboard. Again, the Neutral bonds to a grounding electrode often at the meter base. DONT FORGET TO BUY AND USE GFCI circuit breakers!!!!! !!!!! !!!!! !!!!! !!!!! !!! Now you gotta decide if you want only the 30 amp RV outlets or them plus the 15 amp convenience outlets at each station or wanna go whole hog and run 50 amps to each station CUZ THEN YOU NEED A 200 AMP SERVICE N PANEL !!!!! Best wishes n God Bless John T Retired Electrical Engineer