Tool Talk Discussion Forum
Table Saw Motor trips GFI
Chris Jones
08-05-2006 20:21:19
My capacitor start 1/2 hp 8.8 amps @115 volts motor got really hot the other night and the ground fault outlet it was plugged into tripped. I couldn't get it to reset even with the switch to the motor off (hot wire switched as it should be) I unplugged it and decided to just let the motor cool. Well 2 days later I plugged it in and the motor started fine. I turned it off and turned it back on and it tripped the GFI. Long story short some times it trips the GFI sometimes it doesn't. Sometimes just having it plugged in will trip it even if the switch is off sometimes it trips when the motor is switched on.
Any ideas what could be wrong with it? How to test it? Ect.
Chris Jones
08-09-2006 19:32:26
 Re: Table Saw Motor trips GFI in reply to Chris Jones, 08-05-2006 20:21:19
Well it took awhile to finish that project. I had it disassembled so I cleaned it good then reassembled it. I tested continuity between the case and hot and between the case and neutral and showed infinite resistance. I then plugged it in and repeatedly tried to get it to fail. It's working fine. Well, like I said I'd settle for mysteriously starting to work.
MarkB_MI
08-10-2006 03:52:25
 Re: Table Saw Motor trips GFI in reply to Chris Jones, 08-09-2006 19:32:26
Thanks for posting your results. It's always good to hear how things turn out.
Chris Jones
08-06-2006 09:44:30
Everyone,
The switch is kinda interesting. The motor has a cord but no switch of it's own. The table is homemade and it has a heavy power cord coming from it with a light switche that controls a receptical that the motor plugs into.
Ok.
Table unplugged from GFI.
Saw plugged into table.
Switch on table off.
Plug table in and GFI trips.
Strange.
Ok.
Unplug saw from table.
Plug table into GFI.
Everything is fine. Switch on or off.
Continued by plugging saw into table with switch off.
GFI trips.
Confirmed Hot is the switched wire. Didn't think GFI would care about neurtal. Strange.
I moved the motor to a work bench for further testing. Different GFI receptical at that bench. No switches now involved just plugging it in or unplugging it. And well you know the story.
I will check continuity but as I was holding it on the bench barehanded to prevent startup torque from flipping it onto the floor I don't expect to find the case connected to either hot or neutral.
I disassembled it late last night. There is a LOT of dust and junk in it. I am going to blow it out but I'm skeptical if that will help. I'll post back after my examination today. Oh, I'd kinda think I'd smell something burnt if the field coils were fried. Hopefully I'll find an answer but I'll settle for it working again mysteriously.
tech4
08-06-2006 10:05:09
 Re: Table Saw Motor trips GFI in reply to Chris Jones, 08-06-2006 09:44:30
I think you are going to find that the motor winding has leakage to the frame. You will also find that you have a slight voltage difference between your safety ground and neutral although they are tied together in the panel. The GFI senses current flow that differs between the hot and neutral. When you plug in and the neutral that is not switched lets a small current (enough to trip the GFI) through the winding and the safety ground. You need a new motor. If you had a double pole switch that also switched the neutral then it would not trip with switch off but the motor would still be bad.
bhb
08-06-2006 08:26:28
Your outlet is a groung-fault circuit interrupter or GFCI. A GFCI measures the current comming in the line side and leaving the neutral side. If there is a difference of 4mA to 6mA the outlet will trip. The difference of the current will exit through the ground or if the appliance is not grounded it will exit another way such as a person. Some motors that draw high current will trip the gfci on start up. There are exceptions in NEC 210-8 for gfci circuits.
dr.sportster
08-06-2006 05:49:49
If its doing it with the switch off then its from the switch to the cord to the plug.At least in normal troubleshooting but you may have some new leakage in the motor from the heat.If it was me I would place a wiggy from frame to ground and if no voltage I would use a regular receptacle.Dont quote this when you get electrocuted.To trouble shoot this first disconnect cord at switch plug in;trips bad cord.No trip; reconnect and look for metal chip or foriegn dust in motor.Again may not apply here because you know it go too hot and now something broke down and leaks slight current.To continue job [before getting fired for taking too long] I would now lose the GFI.Not the best advice but thats what keeps the job going.
Dusty MI
08-06-2006 05:40:50
I would think most any capacitor motor motor would/could trip a GFI. Capacitors temporary absorb electricty, GFI's trip if there is more going out than comming back.
Dusty
MarkB_MI
08-07-2006 04:07:54
 Re: Table Saw Motor trips GFI in reply to Dusty MI, 08-06-2006 05:40:50
Dusty,
Capacitors store energy, not "electricity". A capacitor in the circuit will not cause a difference between the current going into a load and the current going out.
Kirchoff's Current Law states that the sum of the current going into a node must be zero. The motor is a node. If the current on the hot side is different than the current on the neutral, there must be another path for the remaining current. Which is pretty much the definition of a ground fault.
Chris Jones
08-06-2006 09:15:36
Yea, that ran through my mind too but since it's run fine for years on a GFI receptical I guess not. Still I'm with you it makes sense it would and yet it doesn't--er used not to.
Dick2
08-06-2006 04:55:04
Did it trip the GFI when it tried to start or after it was up to speed and running? If it tripped trying to start, it could be capacitor or starting switch. As it is inconsistent, sounds more like the starting switch. If you know how to mark the end bells and take the motor apart, sometimes all that is needed is to sand the starting switch points with emory cloth - or sometimes a new switch.
If there is any type of "growl" when the motor is running, it could be a bad bushing/bearing or a shorted coil; then it's cheaper to buy a new motor than repair it.
Chris Jones
08-06-2006 09:18:12
 Re: Table Saw Motor trips GFI in reply to Dick2, 08-06-2006 04:55:04
Sometimes it would trip when I plugged it in even though the motors switch was off. Sometimes it would trip it during start. Once running it doesn't seem to trip it.
MarkB_MI
08-06-2006 04:41:38
You need an ohmmeter. Any multimeter, digital or analog, will do. Read the resistance between either side of the plug to the chassis of the motor. Anything other than an open circuit (resistance = infinity) will cause problems with your GFI. Note that you can't touch the tips of your meter leads while you do this, as your skin can conduct electricity.
Once your confirm that you have leakage in the motor, start looking for the source. It might be something as simple as sawdust in the motor. Hopefully it's not the motor windings, as you would have to replace the motor.
Note that if the outlet is dedicated for the saw, code does not require a GFI.
T_Bone
08-07-2006 03:50:33
 Re: Table Saw Motor trips GFI in reply to MarkB_MI, 08-06-2006 04:41:38
Hi Chris,
Mark's first parragraph has given you the best way to check for nussience tripping. I like using a analog meter myself with a 20megohm scale or more.
With the meter set too 20megohm or higher, I ground one test lead to the motor case then hold the other test lead between my fingers while touching the motor case with the opposite hand. This should give me a meter reading of high resistance telling me I have a good enough ground for winding testing. No meter reading ?, then check the frame ground test lead and repeat.
I then test each motor lead, common, start, run. A slight reading on any motor lead says the winding insulation is starting to break down or contains alot of moisture.
In a open air cooled motor, I would then tend to dry out the winding before condeming the motor. Bake the motor in a oven at 300� for 24hrs as this will boil off any water content. Retest the motor leads again.
If this is indeed your problem, just remember that August is generaly the highest humidity month that we have.
T_Bone
Bob
08-05-2006 21:29:06
The old standby test was to use a "Megger" to test the insulation resistance of the motor for leakage to ground.
Nowadays, there are other electronic AC leakage potential testers on the market.
An electric motor shop should be able to check it out for, the heck of it is, repairing the motor likely would cost more than replacing it.
That being said, high starting current motors can cause freaky things with GFCI's, but the way it sounds it DID work OK before you overheated it, and DOES trip another GFCI, so you have pretty much answered your own question... the motor is "toast".
Hal/WA
08-05-2006 21:00:06
I would try installing a new GFI outlet. If that one trips too, you have something that needs attention with the motor. If the new GFI doesn't trip, the one you replaced has the problem. GFI's are lots cheaper than motors... Good luck!
Chris Jones
08-05-2006 21:13:55
 Re: Table Saw Motor trips GFI in reply to Hal/WA, 08-05-2006 21:00:06
Good advice but I tested the motor removed from the saw on a work bench which uses a different GFI outlet. So it isn"t the GFI outlet. Wish it was.
rustyj14
08-14-2006 14:39:32
 Re: Table Saw Motor trips GFI in reply to Chris Jones, 08-05-2006 21:13:55
I installed one of those GFI things in the extension cord box that i plugged my electrical tools into when working with them. Every time i tried to use an electric drill, sabre saw, or anything else, that danged thing would trip. after 3 weeks of that happy HS, i took out that thing and it now reposes way out in the woods! And, that was 10 years ago or more, and i'm not electrocuted yet. And, since i've retired from my regular job, which never had GFI circuits (weren't heard of back then--did electricity change, somehow, making it shock ya easier??) I only use mostly air powered tools, with the exception of a scroll saw, so i don't worry about GFI. Of course, if i use electric tools outside, i never lay or sit on bare ground because that could get ya fried! But, there are many more fools that do strange things with electric tools, and, with the proliferation of home work shows on TV, i suppose more do it yer-selfers can and do get fried! When i was a wee tot, my family had a Philco radio that ran on 110 volts. It was in a tin case. One day my Dad had the lid off, and when he saw me looking inside, he told me not to touch anything in there. Now, in my 3 yr. old wisdom, i poked my finger at something and promptly got shocked--not badly, just a sharp tingle! That eddicated me to honor anything electrical! Quick lesson! And one i never forgot!