Tool Talk Discussion Forum
Electrical Plug on Arc Welder - Update
Quebec Bob
06-02-2006 04:31:23
I appreciate the quality input from you all. Lots to learn here for me. The panel was installed by an electician; I checked last night and the breaker for the air compressor is a 30 amp (the electrician installed the compressor receptacle too) and here is what is written on the welder: "PRI volts 230-0 CV / 78 arc volts / 25 PRI Amps / 65.7 sec / Amps 230 / Temp rise 115degrees C-60 / Cycle Single Phase". I presume the most relevant spec here is the "25 PRI Amps" which puts me safely in the limits of my 30 amp breaker?
To those of you who say to just lengthen the welder cords, I agree. Here however, I needed more length of cord from the welder to the receptacle because of my barn configuration so I had no choice but to extend that cord. Trying to save money where I can, I wanted to reuse that original welder plug cord so I installed the plastic junction box to make the joint in the two cords (the old 5 footer from the welder and the new 20' extension to the welder). As it turns out (as usual) the whole thing could have been simpler if I had run a new extension cord straight to the receptacle (minus the junction box, etc.) but like most amateurs, there was a lot I didn't know. And now I have to change the plug after all anyway since the 2 male leads run vertically and not horizontally.
BobReeves
06-03-2006 17:11:45
 Re: Electrical Plug on Arc Welder - Update in reply to Quebec Bob, 06-02-2006 04:31:23
I have a 230 amp buzz box on a 50 amp circuit so the electrical police are happy.. however.. I seldom run it over 100 amps, actually don"t remember ever going over 90.. Point being at 90 amps your 30 amp circuit will be adequate and you can do allot with 90 amps.
Stan in Oly, WA
06-04-2006 02:13:15
 Re: Electrical Plug on Arc Welder - Update in reply to BobReeves, 06-03-2006 17:11:45
Hi Bob,
I gave Quebec Bob almost exactly the same advice as yours on the first go round of this issue (three topics below) but the consensus has been running almost unanimously in favor of Bob doing it 100% right, and not one iota less. Warnings of fire and voided insurance policies have been raised. There's really no arguing with that. Personally, if I had enough money and a high enough gag reflex to do everything just the way people tell me I'm supposed to, I wouldn't anyway. But that's my path, and not one I can very well advise anyone else to follow.
All the best, Stan
David - OR
06-02-2006 06:58:26
I fear that Quebec Bob incorrectly parsed the data plate from this welder.
I believe it should read more like:
Pri volts 230
Arc volts 25
Pri amps 65.7
Sec amps 230
Temp rise 115 degrees C
60 cycle single phase
The primary current is thus 65.7 amps, which is what I would expect for an older transformer-based 230 amp machine. 25 amps is an awfully low primary current for that 230 amp secondary rating.
The NEC (national electrical code) has special provisions for branch circuits dedicated to welders (article 630). I expect the CEC is similar. The data plate amps may be de-rated by a factor determined by the data plate duty-cycle. A welder with a 50% duty cycle may be serviced by branch circuit conductors rated at 0.71 times the nominal primary current of the welder.
So a welder with a 65.7 primary amp data plate with a 50% data plate duty cycle (or an inferred 50% duty cycle based on manual operation) may be adequately serviced by a 50 amp branch circuit.
But a 30 amp circuit is too small.
Quebec Bob
06-02-2006 07:25:44
 Re: Electrical Plug on Arc Welder - Update in reply to David - OR, 06-02-2006 06:58:26
When you say it is too small, do you mean that the 30 amp breaker will just have a tendency to trip? Or am I in a dangerous situation here, where I would be better to change the breaker now to a 50 amp? Can I use it safely as is and if it trips too often then switch it to a 50?
paul
06-02-2006 21:58:00
 Re: Electrical Plug on Arc Welder - Update in reply to Quebec Bob, 06-02-2006 07:25:44
Breakers only protect your wires. Technically they don't protect your equipment. Breakers are sized to what your wires can carry. (This is not 100% true, but mostly.)
So, one of the most dangerous things you can do is 'just replace the breaker'. Then your wires will overload, & get hot, and melt, and start a fire.
Maybe.
You already created a problem by extending the wires. Longer runs require bigger wires, or smaller breakers. _Perhaps_ extending your 5 foot run to 25 feet didn't matter - but then again, did you look it up? You get into a voltage drop situation. The longer the run, the fatter the wire needs to be.
Basically to do this right, you will need to throw all the wire away from your main box*, start over with proper sized wire, and a proper 50 amp fuse & receptical.
(* - You'll have to look up your wire size, length of run, & determine if it is adiquate - I don't want to jump to conclusions, but likely a 30 amp circut that you extended to boot will not be able to handle 50 amps.....)
Anything else won't be to code, can void your insurance, and so on.
Aside from all that legal & safety junk that folks don't seem to care about - it won't weld right either, unless you stick to the lowest settings on your welder. So then you are wasting the better part of your welder.
--->Paul
John T
06-02-2006 09:17:59
Like I said, I was surprised if it REALLY only required a 30 amp service ????? ?? but were not there and have to rely on what youre telling us!!!!
To answer your question NOOOOO OOO if it really draws 50 or more amps instead of that figure of only 25 you quoted earlier YOU CAN NOT SERVE IT WITH THAT 30 AMP RECEPTACLE N SERVICE PERIOD
AGAIN many similar 230 amp AC only Buzz Box welders (like the Lincoln if yours is similar sized) require a 50 amp service, meaning a 50 amp 2 pole 240 volt circuit breaker in a panelboard that has the space and ampacity to mount one,,,,, ,,,,three No 6 Gauge wires (2 hot phase wires and an equipment safety ground, often green or bare) ran to a 50 amp receptacle to match the plug on the welder receptacle.
IF YOUR WELDER REQUIRES A 50 AMP SERVICE SIMILAR TO THAT DESCRIBED ABOVE DO NOT USE THAT 30 AMP OUTLET CUZ YOU RISK OVERHEATING THE RECEPTACLES AND WIRES, BUTTTTT THE 30 AMP CIRCUIT BREAKER IN THE PANEL OUGHT TO DO ITS JOB N TRIP OUT TO PREVENT THAT. DO NOT JUST INSTALL A 50 AMP BREAKER USING 10 GAUGE 30 AMP WIRE EITHER CUZ THEN YOU RISK OVERHEATING THE WIRES AND THAT 30 AMP RECEPTACLE
Let us all know, were doing our level best here to help you n keep you safe and comply with the NEC but its tough over the net not being there to go much further
John T, Retired Electrical Engineer in Indiana
Quebec Bob
06-02-2006 09:58:23
 Re: Electrical Plug on Arc Welder - Update in reply to John T, 06-02-2006 09:17:59
Thanks again John. What I am going to do is have the electrician come over and check it out. If that is the outcome of all of this discussion it is a very good one because I did not even know of the safety concerns. I thought that because the air compressor and the welder each were 220 machines, ergo, you could plug them into the same circuit, as long as you were not running them both at the same time. I did not understand the wire size issues, nor that of the breaker. So I'll go on the safe side and have it checked out.
Unfortunately, the information that I listed this morning off the front of the Welder is all printed in two straight lines, without breaks of punctuation (It is an older machine by the way)so it is difficult for me to qualify it any better than the way I wrote it out this morning.
Thanks for all the help. I really do appreciate it from both of you.
John T
06-02-2006 04:59:12
Things are sounding better Bob, thanks for the update. If the welders (just an AC transformer in reality) primary draws 25 amps max which would be if the secondary (welder) is under full load (welding) at the max current, I wouldnt be afraid to use that 30 amp compressor outlet and branch circuit. Just use a plug on the welder to match the receptacle. There are certain NEC rules regarding the max continuous current draw be no more then 80% but thats more like for a 100% continuous duty cycle which that welder would likely not undergo and has its own exceptions as they are not ordinarlly used at the absolute max current with an arc struck CONTINUALLY i.e. they have a way shorter duty cycle. They could likely even overheat if they had a full current arc runnign alllll lllll ll dayyyyy y lol
My guess was right on the air compressor requirements (it being a 30 amp service) but Im still a bit surprised the welder only requires a 30 amp branch circuit as many require 50 amps. If it only requires 30 amps, its inlet cord would be the smaller 10 gauge wires as opposed to 6 or 8 gauge and 50 amp range type plugs Ive seen more often, but thats on the older Lincoln Buzz Box AC welders.
Sounds like your okay, take care now.
John T