Tool Talk Discussion Forum
how many amps is 10/3 wire good for?
Jay87T
10-07-2005 17:02:09
anyone know?
Kevin Bismark
10-08-2005 21:56:18
 Re: how many amps is 10/3 wire good for? in reply to Jay87T, 10-07-2005 17:02:09
If you look at table 310.16 in the nec it say's that nubmer 10 is good for 30 amps in the 60 degree columb, if you are using romex or uf cable you go off the 60 degree columb, the 80 percent if the rating for continous load which we still go by but they kind of got rid of it in the code book, but we still keep the load at 80 percent, if it's a long run you will want to run larger wire...
Kevin
Keith-OR
10-08-2005 18:17:26
Here is a website that you can calculate the info for yourself....HTH..Keith
dr.sportster
10-08-2005 05:44:38
You could also interpert the code as saying a 30 amp circuit breaker but only loaded up to 80% of that or 24 amps.If the circuit drew more than that it would be 8awg.You use only 80% of a circuit breakers rating.So 10 awg on a 30 amp breaker is 24 amps max.
Ken Crisman
10-07-2005 20:34:27
10 gauge is good for 30 amps . But it drops as the lenghth gets greater . 8 gauge is 40 amps . Just make sure all connections are tight . Ken
tra
10-07-2005 20:15:23
Link
Link
Try these.
JL Sargent
10-07-2005 20:05:32
Found this info on this forum:
"My 1999 National Electrical Code book (when I wired my house...) says 10 AWG wire ampacity (with no more than three current carrying wires in the raceway/cable) is good from 25A (for cable type TW,UF at 140 deg. F) up to 40A for the more common types of cable at 194 deg. F. Other, less common 10AWG wire types can handle 60-70W (probably meant to put an A here) at 400F! These figures do not take into account voltage drops across long distances of wire."
Kevin Bismark
10-08-2005 22:02:26
 Re: how many amps is 10/3 wire good for? in reply to JL Sargent, 10-07-2005 20:05:32
If you look in the code book you can't exceed the 60 degree columb in 310.16 so you can only run 30 in a 10/3 romex or uf cable, if you look at that table close it liste the smaller conductors as being limited in current for 14, 12, and 10 wire..
DaveCA
10-07-2005 18:43:52
eveil was correct, he said approximate. It matters where the wire is and what style it is what it is used for and how far it goes.
Need lots more info for correct answer.
JL Sargent
10-07-2005 18:15:01
What voltage?
Jay87t
10-07-2005 18:37:51
 Re: how many amps is 10/3 wire good for? in reply to JL Sargent, 10-07-2005 18:15:01
220v
evielboweviel
10-07-2005 17:06:56
30 amps for a 100 ft or so
Ron
steveormary
10-07-2005 20:37:55
 Re: how many amps is 10/3 wire good for? in reply to evielboweviel, 10-07-2005 17:06:56
Voltage should not make any difference on the current carrying capacity(ampacity) of the wire. 10/3 should be good for 25 amp or a little better depending on use of wire.
steveormary