Tool Talk Discussion Forum
Conecting Generator to Breaker Panel Question
Obie
01-19-2005 05:16:05
O.K. here is another question about our generator.If I turn "OFF" the "Main" 200 amp. breaker in the breaker panel which is right after the power co. meter, then out in my shop I have my electric welding equipment on a 100 amp. breaker disconnect the welder which is (50 amps. at 220 volts)unplug the welder from the "crows foot" outlet and rig up my 6,000 watt 220 v.a.c. generator to connect to that crows foot outlet and feed my ac back to the main panel to feed the well pump and lights in the house and barn. My question is if the main breaker is OFF is that a clean cut OFF and voltage will NOT go out to the power lines? likewise when the power comes ON it will not go to the generator??? Also can I feed curent backwerds thru a ckt. breaker(If its ON ) to feed the other ckt. breakers??
thanks
Ron
buickanddeere
01-19-2005 13:50:43
 Re: Conecting Generator to Breaker Panel Question in reply to Obie, 01-19-2005 05:16:05
I glad to see a vast majority of you fellows have this safety issue sorted out. Thanks to Kim & this site. Some where some day there is going to be more people go home to healthy to thier families.
Eric Skadahl
01-19-2005 09:08:39
Ron
NO NO NO!!! That is not what you want to do. Use a transfer switch that is UL listed. Do not back feed your welder outlet there is no neutral. With no neutral you will have bad line to neutral voltage (120) and you could end up using your ground wire as the neutral, a bad situation. If you want a manual system look up interlockkit it cheep and easy
paul
01-19-2005 07:55:22
This is not a legal way to do it. Some do, but you are in trouble if you get caught. Too many were forgetful and would hurt or kill power line workers. We all take shortcuts with ourselves, but you take on a lot of liability when you start taking shortcuts with other people's lives....
--->Paul
buickanddeere
01-19-2005 07:46:06
I wonder why these home schooled electricians won't take the word of a licensed electrician, the electrical code book and the utility inspector. Do you understand electricity better than the people who write the code book? Just because you haven�t found the time and money for a proper transfer switch and now the pipes are freezing. It doesn�t make it right to back feed a receptacle. If you have a couple of days I can draw out the math and set up a demonstration lab. To show how dangerous �opening the main� or backfeeding a three prong plug to supply 120/240V loads.
Mike M
01-19-2005 09:41:36
 Re: Conecting Generator to Breaker Panel Question in reply to buickanddeere, 01-19-2005 07:46:06
When you get that demo worked up send it to Generac as some of their transfer switches are the same as just flipping a breaker with only a interlock added to keep both from being on at the same time.
dr.sportster
01-19-2005 07:52:13
Buick,Please tell them that pulling the meter does not prevent backfeed situations.Hey guys the neutral has continuity through the meter pan.
buickanddeere
01-19-2005 13:44:03
 Re: Conecting Generator to Breaker Panel Question in reply to dr.sportster, 01-19-2005 07:52:13
I've never seen one of those tied breaker inventions. It gives break before make transfer but I don't know what they did with the neutral. They may have used a three phase panel with the third bus for the neutral? I'll look into it. I have no idea why people let themselves get talked into an emergency panel? Looks great to show your friends I guess. Put in the cheaper meterbase transfer switch and purchase a bigger generator and come out costing the same.
As for why. This is like the kids asking why they can't go out late and hang around with the local riff raff. The kids are just as set on going out as the backfeeding generator user. They will listen and keep asking questions until they can find a half true reason why it's ok.
The "neutral" is a insulated current carrying conductor. No different than the 120,277 or 347 lines. It just happens to be the safest one to tie some part of the transformer secondary to ground for safety and fault protection. You could just as easy tie one of the 120V lines to ground and float the other two. Only problem is that you could get bitten with 240V to ground from one line and 120V from the other line to ground.
dr.sportster
01-19-2005 07:41:36
You will back feed current on the nuetral.The power companies dont just think this up to make people spend money.They are trying to keep linemen alive.
Gerald J.
01-19-2005 07:22:21
Electrically, opening the main and back feeding a suitably wired (4 wire) receptacle works. Its dangerous as hell. Anyone can go to close the main. If the power is back on that connects the generator in parallel with the power company and they will surely be out of phase and the generator shaft will try to rotate instantly to put them in phase. That can twist off shafts or lay the generator on its side. I've heard of both happening. Then if the generator survives the shaft twisting it will either absorb power from the power company or try to supply the power line, neither of which are within its capability and it will probably burn up.
If the power line was still not energized but there's a lineman working it bare handed when that main breaker gets closed the lineman may not survive. His widow and kids will be looking to you for support the rest of their lives.
A slightly better scenario is that with the main closed you supply a dozen neighbors with power an that overloads the generator AND your wiring which can lead to the destruction of the generator an the wiring igniting the house. Neither a great result.
Interlocking two breakers in a box with a mechanical interlock IS acceptable by the safety code. But that means the breakers have to be in the SAME box and you can't use your welder breaker as the alternate feed for your panel because the interlock would keep you from using the welder with the main breaker on.
The dedicated transfer switch between the meter and the main panel is the least confusing option and works well.
Gerald J.
lucasss
01-19-2005 07:11:51
i would reccomend pulling your electric meter if your foolin around with your service.only absolute way to disconnect your panel from the pole.. lucass
Red Dave
01-19-2005 06:33:51
I've seen it done, and I know of some who still do it that way.
But it isn't legal anywhere I know of and if something goes wrong you will have an enormous amount of liability.
My reccomendation is: Don't do it, buy and install a proper transfer switch.
John *.?-!.* cub owner
01-19-2005 06:25:26
Obie, it will work assuming you have a neutral going to your shop so you have 110 for the lights, etc. that need it. Many of the newer transfer switches also open the ground, but the older ones did not. One thing to consider is that it is a vioaltion of electrical codes since you do have the ability to connect the generator while the main is still closed, thus creating a back feed.
Butch(OH)
01-19-2005 06:11:12
I am no eletric expert but I do know how my place is wired (all done by professionals and inspected less than three years ago) and the talk here about grounds and nuetrels confuses me. Now dont jump on me guys but tell me where I am wrong here. There is only three wires feeding my 200 amp house service from the transformer two insulated and one bare I get 220 by using the 2 insulated wires and bare wire and 110 by using one insulated and the bare one right? His generator set puts out 220 across two wires and a ground, nutrual or whatever. Same generator puts out 110 by using one of those wires and same ground (nuetrual or whatever) SO how is backfeeding a 220 breaker with the welder plug going to give wild 110 voltage readings? Not saying it is according to hoyle or code, simply asking about volts here. I agree that the chance you will forget to turn off the main is not worth someones life. When I need to run my small generator I dissconnect the wires I need to run at the servise breaker and wire them to the generator.
MarkB_MI
01-19-2005 06:33:30
 Re: Conecting Generator to Breaker Panel Question in reply to Butch(OH), 01-19-2005 06:11:12
Butch,
You make some good points. In a properly wired house, you should see no difference between the voltage on the neutral and ground. That does not mean it is safe to treat them as interchangeable. The heavy, bare wire coming into your house is a neutral, not a ground. You'll notice that it is just as big as the two ungrounded connectors. At the main disconnect, the neutral and ground are connected, but are isolated in the rest of the system. If you backfeed through the welder, you are expecting the welder ground to substitute for neutral. This might be OK if you know for certain that the ground is a heavy enough conductor to handle the current, and that it is actually connected properly to neutral. More likely, the ground is too small, poorly connected or just plain missing. This would present no problem for the welder, but it will raise havoc if you try to backfeed through the ground. Better to use a disconnect switch, as suggested earlier.
Butch(OH)
01-19-2005 07:02:51
 Re: Conecting Generator to Breaker Panel Question in reply to MarkB_MI, 01-19-2005 06:33:30
Thanks Mark, now I understand why I cant use the wires, or terms interchangably.
paul
01-19-2005 08:15:46
 Re: Conecting Generator to Breaker Panel Question in reply to Butch(OH), 01-19-2005 07:02:51
You have 2 hot wires of 110 and a neutral coming into your service. You do not have a 'ground' wire coming in.
The nuetral wire is used to complete the 110 loop. It may not be present in a true 220 socket.
The ground wire (bare) is there _only_ to protect you, me, your wife, kids, the neighbor from frying. It also provides a quick short & causes the breakers to pop right away, which helps prevent some types of fires & such. It is grounded to earth locally, and also bonded to the nuetral wire at one spot in the main box of your service. (This confuses people and they thing the ground & neutral wires are the same thing....)
In a perfect world, that bare ground wire will _never_ be used by anything, and could be totally eliminated. It is like an insurance policy. It is there but you hope you will never need it. If you do need it & it is installed wrong, like insurance, you will be very sorry.
If the ground wire is ever used for a neutral wire, it turns the entire ground system into a neutral system - which does carry current! That totally voids the safety of the ground system, and allows all sorts of possibilities - such as stray current or a broken wire to energize the metal outsides of all your stoves, washers, driers, drills.....
It is so easy to hook a water system together & see if it works. If not, try again.
With electricity, it is real easy to twist wires together & make it work for 50 years - an electric 110 curciut only needs one live wire and some path to ground - will appear to work fine..... But if done wrong, it is real hard to see that, and a time bomb is waiting to go off. Might not get you, might not ever get anyone. Or, it might kill someone's kid 30 years from now.....
Sometimes the Code seems a little overbearing, but it is there for a reason - usually learned at the expense of people or buildings....
Just explaining, not preaching. :)
--->Paul
Mike M
01-19-2005 06:48:57
My neutral comes into my house and the hooks to the lug inside the box right where the ground wire from the outside ground stake also hooks ??
paul
01-19-2005 08:24:45
 Re: Conecting Generator to Breaker Panel Question in reply to Mike M, 01-19-2005 06:48:57
Yup. That is the _only_ place they should ever be connected.
From there, they go on to do 2 totally different things, and should never be connected to each other again. Beyond your breaker box, the nutral is used to carry electricity, and the ground wire is used to protect things.
If you cross them, the ground wire now is conducting electrity, and makes all of your appliances 'hot' at certain times. Very dangerous.
It would be like saying the fire sprinkler system and the rest of the water system connect near the water main coming into the building. So can you tap off the sprinkler system lines just because the pipe is handy to add toilets, garden hose, lawn sprinkler system?
No, because some fire systems don't have water until there is heat, and even if pressurized if you take away water the pipe will be sized too small & not have enough flow/pressure to run the sprinkler. You might not ever notice the 'problem', but if you have a fire you will be real sorry.....
Sorta like that.
--->Paul
Mike M
01-19-2005 09:49:50
 Re: Conecting Generator to Breaker Panel Question in reply to paul, 01-19-2005 08:24:45
How would they be separate when the box, and the ground lugs are uninsulated and all run together connected together on both sides with a strap ??? All this is hooked to the ground stake and the neutral wire or so it appears ?
paul
01-19-2005 16:32:47
 Re: Conecting Generator to Breaker Panel Question in reply to Mike M, 01-19-2005 09:49:50
Just like your hot water pipes & your cold water pipes in your house connect to the same main water supply. Yet they do different things, and cannot be interconnect later on downstream. Right?
The neutral wire goes from the main box collecting voltage from your appliances & such and returning them to earth. This is often a bit thicker wire, esp for heavy loads.
The ground wire goes from the main box and attaches to all bare metal all over, and is used by GFI equipment to bleed extra, stray, or dangerous electricity back to ground. This is often a bit thinner wire, same size all through the building.
With your water system, if you interconnect your hot & cold pipes all throught the house, you will still have water pressure at each faucett. But, it will not be the good cold or good hot water you expect - results will be odd to say the least!
Same with the ground & neutral - yes you can interconnect them throught the house, and you will have voltage at all outlets. But it is _not_ the results you want to have - just like interconnecting hot & cold water pipes willie nilly....
--->Paul
Mike M
01-19-2005 18:55:55
 Re: Conecting Generator to Breaker Panel Question in reply to paul, 01-19-2005 16:32:47
Your water system would be like DC current an entirely different system.
david - OR
01-19-2005 06:27:05
The equipment grounding conductor for a welder circuit could be as small as a 10 AWG wire. Uncomfortably small for this use. Or there could be no equipment grounding conductor at all if the welder outlet was wired with conduit.
All of the unbalanced neutral current will have to flow through a path which was never intended for anything but a safety ground. If the generator has a relatively high output, and if the loads are distributed unevenly, then the more heavily loaded 120V side will be at too low a voltage, and the more lightly loaded side will be at too high a voltage. The exposed metal of the welder outlet may be at a voltage above ground, creating a safety hazard.
It sounds like the orignal example may involve a sub-panel in a remote building, which is even worse.
Mike M
01-19-2005 05:39:52
This is another one of those questions that will bring you all kinda answers. Some say it will still backfeed others have been doing it for years. Funny thing is that if you go buy the $300-$400 transfer switch panel from Generac it is basicly just flipping on and off breakers the only differance is that they have a little metal bar that slides back and forth acting as an interlock so you can't have both breakers on at the same time.If flipping a breaker can still backfeed out the ground someone better explain this to Generac Corp. so they can recall these.
paul
01-19-2005 08:29:05
 Re: Conecting Generator to Breaker Panel Question in reply to Mike M, 01-19-2005 05:39:52
I guess that is like saying the only difference between diesel fuel & gasoline is a few btus....
There is a little more to the story, and a lot of people's saftey relies on the 'tiny' details.... :)
--->Paul
MarkB_MI
01-19-2005 05:33:38
Do not backfeed through your welder plug. This outlet has no neutral connection, only two hot lines and a ground. You will get 220 volts between the two hot sides, but what you get on each individual 110V phase is anybody's guess.
I'll leave it up to others whether or not it is EVER safe to backfeed through a breaker, but you definitely should not do it through a welder outlet.
Jimmy King
01-19-2005 05:31:23
I don"t know what they cost now years ago $100, a double throw switch box that goes right below you meter. Down is alt. up is on line, and the middle is off, they are the only thing an electric co will ok and by far the safest. With it there is no chance of back feeding, and killing a lineman working on the line. It also will have a line and plug for your alt.