I have a furnace (boiler) that seems to have a thermocouple failure once a year. Boiler is natural gas. Has been converted from LP, but I don't know that that should make a difference.
Other furnaces I have or am familiar with go years without needing a new one.
Any thoughts? Thanks
bhb
12-23-2004 15:10:00
 Re: OT? Furnace Thermocouple Life? in reply to Dave ( IL), 12-22-2004 17:54:16
Two important things to check are the amount of the thermocouple that is in the flame and the quality of the flame. The thermocouple generates electricity by the heating of two dissimilar metals. The metals are in the tip of the thermocouple, the outer copper tube is one conductor and there is a wire inside that is the other conductor. If not enough of the tip is not in the flame the thermocouple won"t generate enough elctricity to hold the gas valve pilot solenoid open and it will close and stop the gas flow through the gas valve. The pilot flame must encase the thermocouple. The flame should contact the end 1/4 to 1/2 inch of the thermocouple. Follow the manufacters recommandations. If not enough of the thermocouple is in the flame it won"t generate enough electricity to hold the pilot solenoid open. If to much of it is in the flame it will overheat and burn the thermocouple.
Check the pilot flame it should be a blue flame. If it is yellow or partly yellow you will have to take the pilot assembly apart and clean it. Fine dust and lint will block the air to the pilot. This is more prevalent on boilers and counterflow furnaces because the burners are closer to the floor. Furnaces don"t end up in the cleanest rooms in the house.
I have been in the HVAC industry nearly 40 years and haven"t seen a furnace blow up do to the pilot going out and the burner staying on. I am not saying it couldn"t happen but I haven"t seen it. I have seen gas valves stick open usally do to pipe joint compond in the valve. Gas appliances are probably safer than the tractors we play with.
Jay (ND)
12-23-2004 21:23:28
 Re: OT? Furnace Thermocouple Life? in reply to bhb, 12-23-2004 15:10:00
Nice. Pilot out, no boom usually means bad thermocoupler and pilot needed cleaning. Boom means bad valve and tenant was going to call right after turning on the lights.
T_Bone
12-23-2004 20:47:41
Hi bhb,
For the sake of this discussion, lets assume we have a single stage gas valve and need to install a thermocouple.
1) Please list the install procedures for the thermocouple?
2) Please list ALL tests that the thermocouple must pass after it has been installed and give a brief over view of that test?
3) Please give a brief explanation of how this gas valve orperates?
I will give you my follow up post after you answered these basic questions!
Retired member of ASHRE (American Society of Heating And Refrigeration Engineers)
T_Bone
MarkB_MI
12-23-2004 18:19:39
Excellent explanation. All these years I thought it was magic.
Dave ( IL)
12-23-2004 08:51:47
Thanks everyone.
T-Bone, I hear you. Boiler is about 12 years old. Conversion is 9 or 10 and was from LP to natural. Mfg's conversion kit was used. I know that had new jets, but I can't remember if it included anything new for pilot. Thermocouple problem is "new". Gas company has been out twice to light it - once on original conversion and two years ago when gas was shut off for a short time.
Going to call gas company just to be on safe side.
Thanks again. Dave
T_Bone
12-23-2004 01:15:26
Hi Dave,
Sounds like to me who ever did the conversion from natural gas to LP gas didn't set the correct pilot flame impringment onto the thermocouple.
This does two things:
1)it severely shortens the life of the thermocouple
2) When the pilot flame goes out, the main gas valve is held open to long thus dumping a extra raw gas into the burner area and defeats the saftey factor of using a thermocouple.
As you can see reason #2 is of a huge concern as it could/will cause a explosion.
This problem is way beyond the scope of this forum and you need to call a service tech. I suggest calling the gas supplier as they will test the thermocouple for proper orperation since it was clearly not done during the conversion setup.
If you listen to the responeses below, you will get someone killed!
Please get this taken care of as soon as possible as this isn't a small problem that can wait!
T_Bone
MarkB_MI
12-23-2004 18:23:50
 Re: OT? Furnace Thermocouple Life? in reply to T_Bone, 12-23-2004 01:15:26
T-Bone,
I was with you up 'til your #2. I'm afraid I don't understand why a misadjusted pilot would cause a hazard. Could you elaborate?
T_Bone
12-27-2004 20:59:53
 Re: OT? Furnace Thermocouple Life? in reply to MarkB_MI, 12-23-2004 18:23:50
Hi Mark,
There's many different types of gas valves, varible volume, constant volume, multi-stage and single stage and just as many control designs. These type of vlaves can be found on residentual heating units and probably a few more as the burner units get more efficient.
For this example I'll use a simple single stage gas valve with thermocouple.
A typical thermocouple generates 350mv when heated to design tempature. This voltage then is appiled to a coil on the main gas valve holding the valve open so a volume of gas can flow to the burners.
If the thermocouple has too much heat beyond it's design limit, then it will not cool down fast enough to quit generating electricity thus holding open the main gas valve too long dumping excessive raw gas into the combustion chamber.
For the sake of this discussion, lets say the mfg designed the combuston chamber for when the thermocouple at correct design tempature would allow .125cf of gas into the combustion chamber upon pilot flame failure.
Now lets heat the thermocouple to twice the mfg design flame impringement length. In the real world it will take approx 3times as long for the thermocouple to cool down and shut off the main gas valve and now .5cf of raw gas is now dumped into the combustion chamber upom pilot flame failure or 4 times the mfg limit for the combustion chamber design.
There are tests that have to be completed on a typical thermocouple system to insure the thermocouple is installed correct. To many variables in both parts and controls to cover here and is why there's books written on the subject that can't be covered on the internet.
4 times the gas volume beyond mfg design is alot of BOOM!
T_Bone
T_Bone
12-23-2004 20:49:27
Hi Mark,
Hang tight as your question will be answered shortly.
T_Bone
msb
12-22-2004 20:13:23
You might want to move the thermocouple so it isn't directly in the middle of the flame.I have done that with good success on grain dryers to extend the thermocouple's life
lucass
12-22-2004 19:48:00
my new furnace tcouple lasted 3 years, the replacemant tcouple has been goin 15 years... i wish i knew the reason they go bad.have rental properties and have never put one in a water heater. lucas
JOHNK
12-22-2004 18:15:00
Do you mean you have to replace it or relight it once a year.Use a good brand (Honneywell),the flame only need's to be large enough to light the burner and keep the pilot coil energized.Bigger is not better in this case.They last forever in the hot water heater's.
Dave ( IL)
12-22-2004 18:24:53
 Re: OT? Furnace Thermocouple Life? in reply to JOHNK, 12-22-2004 18:15:00
Replace. Third one in as many seasons.
My other experience is maybe 2 or 3 in 30 plus years of various furnaces and hot water heaters in 5 different houses.
Rusty Scupper
12-23-2004 09:32:26
 Re: OT? Furnace Thermocouple Life? in reply to Dave ( IL), 12-22-2004 18:24:53
Mine lasted 6 years on a new furnace. My repair guy said that was close to a record on that furnace. Purchased a spare to have sitting on the shelf. We all know it will go out on the coldest night of the year which will also be a holiday.