Wiring for shop
Steve-Maine
12-16-2004 03:00:53
I'm getting ready to finish wiring my new shop and am confused on wiring to compressor, I have been looking at 12-2 with ground or 12-3 with ground. Can you use 12-2 with the ground wire as neutral. This is a 220 line, Thanks
Big Jim
12-17-2004 00:05:33
 Re: Wiring for shop in reply to Steve-Maine, 12-16-2004 03:00:53
Buckanddeere is right. There is no substitute for knowledge and experience. If that won"t fly, at least ask your local inspector what is required. Local jurisdictions have the authority to adopt requirements more stringent than the NEC. I believe residential applications are now required to run a neutral and ground for all 240 volt circuits so that could be an issue. Personaly, if it"s 240 split phase, I always run 3 wire + ground. Cost difference is neglegable and I covered for anything in the future.
buickanddeere
12-16-2004 12:05:30
As a licensed industrial and construction electcrian. As soon as I see questions like that the person should hire a pro. Trying to save a few dollars D.I.Y is going to cost you more than having it done correct the 1st time.
john in la
12-16-2004 10:58:12
While you did not give all info needed (size of motor; distance from box to plug; ect) to give you a answer lets look at some general points.
All 220 compressors I have seen run only on 220 and do not have any 110 parts so they have a 3 post plug.
For this type of set up you will need 2 hot wires and a ground. No neutral needed.
I use 10-2 w/ground as a minimum on 220 stuff.
A neutral is used when you have 110. On a 4 plug 220 outlet like a dryer you have 2 hot 1 neutral and 1 ground. The reason it needs the extra wire is that dryers have some parts that run on 220 and some parts that run on 110.
A neutral is only needed to make 110 and you should never use a ground wire as a neutral or a neutral wire as a ground. They are not the same or interchangeable.
FarmerDave
12-16-2004 13:14:28
 Re: Wiring for shop in reply to john in la, 12-16-2004 10:58:12
Some day somewhere some pin headed engineer is going to decide that he can add a computer to an air compressor. For ten bucks in electronics a 175 psi job just became 180 psi. The catch will be that to run the computer the cheapest way to do it is to start with 120V and rectify it to dc. Now if you wired it with two wires and ground you are SOL.
What does the code call for on a dryer or a range? Can you grandfather a three wire 220 circuit in there?
FarmerDave
12-16-2004 09:50:05
There's been some good answers given. What's the plug on your compressor look like? Does it have four prongs or three? When you go to get a recptacle for it how many amps does the recptacle claim it's rated for?
Now I have a question. Do they make four prong rectacles that accept three prong plugs. If so would you ever want to plug a four prong plug into the recptacle you're wiring?
txblu
12-16-2004 10:26:08
 Re: Wiring for shop in reply to FarmerDave, 12-16-2004 09:50:05
Not that "I" am aware of, but you can make a short jumper using a suitable conductor if you wanted to adapt one kind of plug to another (as long as you weren't defeating the purpose of the shape of the plug.
Mark
FarmerDave
12-16-2004 11:10:46
 Re: Wiring for shop in reply to txblu, 12-16-2004 10:26:08
Well we all know a 15 A two or three wire plug will fit in a 3 hole 20A receptacle.
I would have suspected a 30A three 220 prong plug would fit in a 4 prong 30 A 220v receptacle. So you have an extra equipment grounding conductor in the receptacle, it could be handy when you unplug one appliance and plug in another. Especially if your wiring a new receptacle.
MarkB_MI
12-16-2004 17:23:18
 Re: Wiring for shop in reply to FarmerDave, 12-16-2004 11:10:46
Understand that there are many kinds of 220V plugs. First of all, there are three prong plugs that have a neutral but no ground; dryer and range plugs fit this category. Other three prong plugs have a ground but no neutral, an example being welder plugs. Consequently there's not a lot of interchangeability between 220V plugs and receptacles.
I believe you can plug a three prong 220V, 15A grounded plug into a three prong 220V, 20A grounded receptacle.
But really the original question has nothing to do with plugs and receptacles. For all we know, Steve wants to hard-wire his compressor to a wall switch.
FarmerDave
12-16-2004 11:45:42
Probably if your wiring a new 220V receptacle/box you might as well run 4 conductors because wire's cheap in comparison to labor and rework charges.
CNKS
12-16-2004 07:43:41
I don't like to take chances -- It also depends on the size of your compressor. I have about a 60 foot run with 8-2 with ground. Getting by with what barely works to save a few bucks is not a good idea.
MarkB_MI
12-16-2004 03:37:24
If you're talking about the connection between a breaker panel and the air compressor, you only need two conductors plus a ground. (In other words, 12-2 will work.) Same with a 220V welder. Let's be clear here: A 220V air compressor does not use neutral! The air compressor equipment ground must be tied back to ground, not to neutral.
You might want to go up to 10-2 for your air compressor if you have a very long run; air compressors have a very high starting current and the larger gauge cuts down on voltage drop.
Now if you're talking about the service from your meter/service disconnect and your shop, you need four wires: 2 "hots", a neutral and a ground. And you'll need a lot more information than I can give you here.
txblu
12-16-2004 06:14:41
 Re: Wiring for shop in reply to MarkB_MI, 12-16-2004 03:37:24
Something to think about. The ground. Where are you going to get it if it is not included in the wiring bundle?
As I recall code requires that the ground have the same ampacity as the conductors so the ground needs to be at least the same cross sectional area and resistance per foot as the power lines.
Additionally, As I recall 12-3 means all 3 conductors are insulated (black, white, green). 12-2 W/ground is also a 3 conductor cable, all being the same size but the ground is bare (black, white, bare). That's the most economical choice as far as I'm concerned.
Also code requres it to be in conduit. HD has nice rolls of MC flexible metallic cable in 12 awg or 10 awg that's reasonably priced and solves all these problems for you. It is 12-3, but still something to consider.
Mark
MarkB_MI
12-16-2004 17:31:30
 Re: Wiring for shop in reply to txblu, 12-16-2004 06:14:41
Mark,
Your recommendation to put the wires in conduit rather than use exposed Romex is a good one. The code requires it, but I know that inspectors generally turn a blind eye to the use of Romex in outbuildings. ("You're going to cover that with drywall, right...") I did my whole shop in conduit. It was a lot of expense and work, but I have no regrets.
One thing I forgot to mention in my earlier post: If Steve uses 12-2 Romex, he should mark both ends of the white conductor with black tape. This is required by the code, and will tip off anyone working on the wiring that both conductors are hot.
Charles (in GA)
12-16-2004 17:29:47
QUOTE... As I recall code requires that the ground have the same ampacity as the conductors.
Not true. NEC table 250-122 requires equipment grounding sized to the breaker capacity, with 15 amp requiring 14cu wire, 20 amp requiring 12cu wire, and 30 to 60 amp requiring 10cu wire. I think the idea is that it merely has to carry the current long enough to trip the breaker.
Charles
Charles (in GA)
12-16-2004 17:18:23
QUOTE... Additionally, As I recall 12-3 means all 3 conductors are insulated (black, white, green).
Actually a 12-3 has a black, white and RED wire. Never seen a insulated green in romex. If its 12-3 w/grd, then you have the black, white, red, and bare.
Charles
galen
12-16-2004 20:27:20
 Re: Wiring for shop in reply to Charles (in GA), 12-16-2004 17:18:23
12-3 is a romex term. Means three insulated conductors, it is available with or without ground iin it. As far as wiring a compressor to recommend a wire size you must know horse power and distance. One more thought on this it is required to have an equipment disconnect with in accessible distant. A plug will work in this situation. These last 2 thoughts are subject to your inspector if required they all havee there own interprutation of the code. Please excuse spelling don,t need it on the job just sweat and no brain
dave blakeman
12-16-2004 07:53:32
In responce to Mark.Conduit is pipe.The code does not require compressors to be wired in conduit.Lots of electrical misinfo is being spewed on varius sites.Also if you have to say"as i recall"then just get your code book out and look it up to be sure.If not youll fail inspection and do it twice.Before all you guys run out and buy the N.E.C.Imust warn you its not written in laymans terms but in electricians"legalise"that one goes to school to understand and interprit.
txblu
12-16-2004 10:20:53
 Re: Wiring for shop in reply to dave blakeman, 12-16-2004 07:53:32
The code my county inspectors uses does. Says he, iffin it is below the rafters and it ain't in MC or so, it ain't a goin to get the green tag. No green tag, no meter says the power co.
Mark
steveormary
12-16-2004 08:49:50
dave, and then you still have difficulty understanding and interpeting the code book. Even the elctrical inspectors cant agree on interpetation sometimes.
Better contact your local inspector or a licensed electrician if you have questions.
steveormary
txblu
12-16-2004 10:23:43
 Re: Wiring for shop in reply to steveormary, 12-16-2004 08:49:50
I happen to have been in the book recently getting my wiring design finished to submit to the county for my building permit.
Even in the book (NEC) they talk about certain editions having certain parts that are pure jibberish that no one can understand on it's own merit; just have to improvise best one can it says therein.
Mark