02-23-2004 21:34:28
I'm the guy about to install a 100 amp sub panel about 40' away from a 200 amp main panel. The calculations I come up with say I can run #8 wire but that seems small for 100 amp service. I normally run #6 for 50 amp service. Can someone double check that number because my book is nowhere to be found.
Mainly, I will be running a 220 volt window unit (20 amp) and 2 ceiling fans, several lights, small hot water heater (30 gallon) and a computer so a 100 amp sub panel should be suffecient and help keep the voltage drops down.
buickanddeere
02-25-2004 12:12:39
 Re: Wire Size in reply to Skinner, 02-23-2004 21:34:28
What are planning on for where and how for grounding? Most applications will allow a #3 copper supply and a #6 bare ground.
Lambchops
02-24-2004 16:49:29
The first thing I recommend is to get yourself an electrical permit. The cost is minimal and as a homeowner you should be able to secure one. Take no chances when it comes to your electrical service. You then should verify any questions you might have with the electrical inspector. Don't be afraid of him, his job is to make sure your home is safe. With that said the correct size wire for a 100 amp sub panel is #3 THWN copper. Run 1-1/4 EMT making sure you have no more than 4 90's. Do not connect the bonding jumper to the neutral bar and if you use concentric knock outs you will also need to use bonding bushings. These are all items to confirm with the electrical inspector because each town/State has different rules in which they follow. Good luck and be safe.
BB
02-24-2004 04:30:58
As Turtle said, there are a lot of considerations when doing your wire sizing. However, this voltage drop calculator can help get you in the ball park as far as size.
rustyfarmall
02-24-2004 04:30:31
I am not an electrician either, but when I did the very same thing just about 5 years ago, I asked lots of questions to qualified and licensed electricians. The answer on wire size was the same from all of them. Minimum number 2. To cut the cost a bit, they all agreed that I could use what is referred to as 2-2-4, that being size 2 for the conductors, and size 4 for the neutral. This is for buried service.
Turtle
02-24-2004 04:21:48
Simply put there is more to figuring conductor size than just looking in the book. You have to know if it is in conduit, open air, number of current carring conductors, etc. A number eight is to small for 100amps. You must also apply the correction factors for the temps. in your area. In this case the distance is nill at 40 foot. With out knowing all the above paticulars, If you are comming from a 100 amp breaker, you will need at least a number 2. Again this is only a blind shot with out the hole story. It's not just what your feeding to but what your feeding with. Spend the extra few dollars and get a professional to cone help you, the insurance company as well as your family will be glad you did.
DaveWis
02-24-2004 02:45:50
I'm not an electrician, but the NEC lists ampacities for all conductors. You must use a wire of sufficient ampacity for the overload device protecting it. For a 100 amp breaker I believe that would be #2 or larger depending on what type of wire you are using. At best improper wiring can cause damage, at worst it can kill. If you have ANY question ask a professional. Please don't gamble with it.
Not much help, but
02-24-2004 00:02:23
the 100 amp sub panel will not affect the voltage drop one way or another. It's the wire size, distance and amount of current draw that determines the voltage drop. A panel with a 100 amp breaker will shut off power if current goes over 100 amps.
See next post. You are in the recommended 5% or less drop using those figures.
Please have your work checked by a licensed electrician or building inspector, especialy for a sub panel.
Skinner
02-24-2004 04:28:25
 Re: Re: Wire Size in reply to Not much help, but, 02-24-2004 00:02:23
Thanks for the info, that is what I needed.
Sure it affects voltage drop, but we probably aren't on the same page. I can run larger wire to the sub-panel, then smaller wire to the plugs and appliances since those distances aren't as far, of course staying within the proper gauge wire for each items amperage. Main reasons is for expandability, and ease. My 200 amp panel only has room for a couple of more breakers, which hopefully I can get a 100 amp double in there, the conduit run will be buried since there isn't a good easy path from panel to panel inside the shop, and it allows the breaker box for that room to be in that room. The room is like a add on living area / entertainment area / Office off my main shop.
Thanks again for the info.....
Richard
Brian G. NY
02-24-2004 16:39:02
 Re: Re: Re: Wire Size in reply to Skinner, 02-24-2004 04:28:25
I used 00 aluminum buried for the 220' run to my shop. You don't need that but I'd go a little heavy, the initial difference in cost is not that terrible and then you won't have to worry about it. I sure like the sounds of the ultimate usage. I hope you have headroom enuf for "the girls on trampolines"!!
Slowpoke
02-23-2004 23:44:01
240VAc/100a/40'/8ga/2.22% drop to 235v.
6ga/1.4% drop to 237v.
4ga/0.88% drop to 238v.
240VAC/50a/40'/8ga/1.1% drop to 237V.
6ga/0.7% drop to 238v.