This is a common technique. I would do the same. The most common error made by homeowners in this case is mis-handling the ground and neutral. The remote panel is a sub-panel. This means that the grounds and neutrals must be kept separate inside the panel, and that the neutral bar MUST NOT be bonded to the cabinet of the subpanel. (The cabinet MUST be bonded to the equipment grounding conductor). You will need to run 4 wires between the two panels. No, you can't just staple up that cheap 3 wire type SE cable from Home Depot. No, you can't drive a second ground rod for the subpanel. No, you can't wrap a separate ground wire around the type SE cable. You need two hots, one neutral, one ground. If you run the wires in metal conduit, theoretically you can dispense with the ground, but I always run a properly sized equipment grounding conductor as well as make every effort to effectively bond the conduit. Be sure to pay attention to the code rules on the placement of panelboards. You need a 30 inch wide space, 36 inches deep, and 6.5 feet high in front of the panelboard. Furthermore, the areas directly above and below the footprint of the panelboard must be clear of pipes, ducts, etc, from the floor to the structural ceiling. Since the subpanel is not a service disconnecting means, you may be allowed to put it in a bathroom, but I wouldn't.