Mike
02-05-2004 06:26:33
Re: Multiple electric branches to a shop. Is it co in reply to Brad, 02-04-2004 20:30:25
To do it right, you have to options. 1. Get a new service, seperate from your house to your shop, this way you will have plenty of power, and will have a panel in your shop. The number 2. option is to run a subpanel from your house. This is not as good of an option as the first, but is probobaly cheaper. put a panel in your shop, figure out how many amps you need, as you will have 220 volt. Then make sure that the total amps needed in the shop wont overdraw your house feed. I it doesent, this is what you do. Say you are going to put a 100 amp sub panel in your shop. you install a double pole 100 amp breaker. you will then run your wire from that breaker to feed your main breaker in the panell in your shop. if you run a 100 amp , the code is #2 wire, i usually bump up a size on my projects, just for safty. The best type of wire to run is called URD, rated for underground direct burial, for more saftey, you can run the wire in PVC conduit, pretty cheap insurance, also, about 1 foot above the wire in the trench, you should lay in a electrical caution tape. This is my advice as how to do it. Mike,Union Electrician