Tool Talk Discussion Forum
Wire size question
chris smith
01-31-2004 09:39:11
Is there a rule of thumb on how big a conductior should be for a given length??? Say a 14 gauge can carry 15 amps.. How far can it adequately do this?? How far before you must go up a size?? How much farther can you go then before going bigger?? Two reason i am asking, i know a 14 gauge will carry 15 amps and 12 will carry 20 aND 10 will carry 30. But i dont know how far it will carry this before needing to be up sized?? Any body explain this to me?? And secondly i was wondering because i saw a moron trying to run a 15 amp air compressor on 200 feet of 12 gauge cord!!!! An couldnt figure out what size wire would be needed to carry it..
Thanks guys!! chris
Slowpoke
02-01-2004 18:48:00
 Re: Wire size question in reply to chris smith, 01-31-2004 09:39:11
Search: MC� Estimators' Reference.
Lots of good stuff.
Lamchops
01-31-2004 14:57:26
The rule of thumb is you would up one wire size for every 100 feet if you are using the wire at full capacity. You also need to only load the circuit at 80% or for a # 14 wire @ 12 amps, a # 12 wire @ 16 amps, a # 10 wire @ 24 amps. Lets say you have a # 12 wire and it's connected to a 6 amp load, you would then be able to have a longer lenght of wire without seeing a voltage drop. Also, when you use THWN wire you'll see that it has a higher rating at 90 degrees C. Let's say that a # 14 wire at 90 degrees C. is rated for 20 amps, now you can't connect that much amprage to # 14 wire because the circuit breakers and wiring devices are only rated at 75 degrees C. But you can use the higher rating for voltage drop calculations, meaning you can have a longer wire run without suffering from voltage drop. Now when you have a motor load, you need to add 125% of the motors running current to your circuit calculation. So let's say you have a motor that runs at 10 amps, multiply that by 125% and you get 12.50 amps. That means you need to run #12 wire on a 20amp circuit.
David - OR
01-31-2004 18:02:45
 Re: Re: Wire size question in reply to Lamchops, 01-31-2004 14:57:26
Uh, sorry Lamchops. You cannot "use the higher rating for voltage drop calculations".
Voltage drop in a wire depends only on the diameter of the copper core of the wire and the length. It is completely independent of the type of insulation on that wire, or what temperature the insulation is rated to. You can't get a longer run out of a given size of wire by using a "better" kind of insulation -- only by upsizing the core of the wire.
Ampacity is a function of insulation type and its attendant temperature rating. As you note, an ampacity listed at 90C is rarely directly useful -- because the terminals it connects to are typically rated to only 75 C.
Where that 90C rating comes in handy is in conduit fill de-rating. Now you can take that 14 AWG wire rated to 20 amps at 90 degrees, stuff 6 of them in a conduit, de-rate to 80%, and still get an effective 15 amp capacity.
Ampacity is a safety issue related to heating of the wires. For this, insulation type matters.
Voltage drop is a performance issue related to supplying enough voltage at the end of the run. For this, insulation type does not matter.
If the voltage drop is so bad that the motor will not start, and sits there and hums while it draws the locked rotor current, then there may be safety issues with both kinds of wire. Hopefully, the motor starter and/or the circuit breaker will trip in this case.
Lamchops
01-31-2004 18:47:40
 Re: Re: Re: Wire size question in reply to David - OR, 01-31-2004 18:02:45
Well now your going to make me work eh? Lets see here if I can remember this correctly. It's been awhile since I served my apprenticeship and I don't have my book handy but here goes. There are 4 things that affect voltage drop: lenght, temprature, type of material and insulation. If you look at the code book you'll see that RH type insulation will have a different ampacity of THWN, both are copper wire but the insulation is the factor. Now I agree that wire fill is the most common use of the 90C but with a little research you'll find that you can use it in voltage drop calculations as well. Now with that said, good wiring design will tell you that it's best to error on the larger wire size when doing voltage drop calculations. The last thing you want is to have a motor try to start in the middle of summer when the power company is already giving you a reduced voltage and damage the windings or burn up the motor. When a motor starts it can draw up to 5.5 times it's running current so I agree with you that when you have inductive loads that it will never hurt to up the wire size. Now what about those capacitive loads and neutral size?? Brian
David - OR
02-01-2004 07:14:13
 Re: Re: Re: Re: Wire size question in reply to Lamchops, 01-31-2004 18:47:40
OK, let's get the book out.
Table 310.16 of the 2002 NEC lists RHW and THWN as being rated to 75c and capable of 20 amps at 14 guage. You were probably thinking of THHN or THWN-2, which are listed at 90 degrees and 25 amps. Type TW is rated to only 60 degrees and 20 amps. There is no RH listed. But I can never remember these without the book handy either.
Voltage drop is not a mandatory code regulated issue, being covered by "Fine Point Notes" which suggest that satisfactory service can be obtained if the total voltage drop is held to 5%, and recommending a max of 3% for feeders and 3% for branch circuits.
Table 8 at the back of the book gives the direct current resistance in ohms per 1000 feet for various wire sizes at 75c. No distinction is made for insulation type, although there is a difference depending on whether or not the wire is stranded.
The simple equation for voltage drop becomes Vdrop = (R (from table) * (length of wire) / 1000 * current). This is what is most commonly used for figuring out if wiring or an extension cord will work, as it is conservative in most circumstances. Don't forget that it is the two-way length that matters -- a 200 foot extension cord is 400 feet of wire from the electron's point of view.
Table 9 of the NEC gives the AC resistance and reactance for various wire sizes and wiring methods (steel vs aluminum vs. plastic conduit). It offers the following equation for computing effective impedance.
Ze = R (from table) * (Power factor) + XL (from table) * Sin(arccos(Power factor)
From the effective impedance and knowledge of the current and power factor you can than compute AC voltage drop.
Insulation type does not impact any of these calculations.
I suppose you could take into account the skinny cross section of wires like THHN, compared to chubby wires like RHW, and argue that the conductor spacing, spacing of conductor to the conduit, the capacitance per unit length, and effective impedance might end up slightly different. But you'd be going on your own, and I don't know how you'd take into account the varying geometry as the wire is pulled through the conduit.
You are correct in noting that resistance is a function of temperature. (It goes up with higher temperatures). Since some insulation types will allow operation at higher temperatures in limited circumstances, you could argue that the voltage drop for the core of a THHN wire should be computed at 90c instead of the 75c for RHW. But then the THHN wire would have a higher voltage drop (and lower serviceability) than an RHW wire, the opposite of what you seemed to be implying above.
Lamchops
02-01-2004 08:42:12
 Re: Re: Re: Re: Re: Wire size question in reply to David - OR, 02-01-2004 07:14:13
They say the first thing to go is the mind. A couple of things first though, I was thinking of TW wire not RH and secondly I was refering to ambient temperature. If you look down table 310-16 (NEC) you'll see the correction factors for ambient temperatures which will have an overall effect on the max amprage of the circuit and also needs consideration in voltage drop calculations. Now I still do not have my book handy but getting back to the original thought and that is without doing the VD calculations the 100' rule is a good reference point. I fully agree that you are not allowed to excede 3% VD on any branch circuit and also agree that when motor loads are used that it becomes even more important to maintain the maximum voltage. I guess my thought that if you are using only lets say 50% of the circuits capacity on a general lighting circuit that you could slightly increase the lenght of the wire without voltage loss. I'm not saying double the lenght but 30% longer would not hurt. I know this has gotten to deep for most anyway but it's fun to chat about it. I'm new to this site and of course my love is tractors. I want to give a little help back to those who have helped me with my tractor issues and of course I want to give good info also. Thanks for your clairifications. Now I better go dig that book out. Brian
buickanddeere
01-31-2004 14:45:00
Rule of thumb is 100 ft for 3% max legal voltage drop for wire at it's rated capacity. Eg. 12 gauge at 20 amp. The inrush current at startup was the down fall of the 200' compressor experiment. A single phase induction motor will draw no less than 6x and up to 15x it's rated current for the 1st couple of AC cycles when energized. And 3x to 8x it's rated current until up to speed. Your buddy was trying to start the compressor with about 190 volts. The motor can't make enough torque in that brown-out condiiton to roll the compressor piston over top dead center. Add to that a reciprocating compressor is the nastiest load bar none to get rolling.