Electric Co-op has agreed to install a new meter base which will allow seperate feeds (200 amps each) for the house and the garage. The garage is approx. 150' from the meter pole. The garage service will run underground.
What is the minimum size and description of the cable the electrician should run?
Thanks!
buickanddeere.... transfe
01-24-2004 05:30:50
 Re: Wire Size for Underground Service to Garage in reply to JimW1950, 01-23-2004 11:39:56
For all those e-mailing and wating to know who and where for the legal/foolproof meter base transfer switch and standby generator plug.
Link
http://www.sommersgen.com/pages/mantrans.htm
Short Round
01-23-2004 17:01:05
Jim, if your electrician does not know the size and type of wire and conduit to run, I would look for some other electrician. Do it once, do it right and be done with it.
The Right Answer nm
01-23-2004 17:23:42
 Re: Re: Wire Size for Underground Service to Garag in reply to Short Round, 01-23-2004 17:01:05
nm
BIG WOOD
01-23-2004 16:46:39
As per NEC 2/0cu 175a 3/0cu 200a 4/0 230a, 2/0 al 135a 3/0al 155a 4/0al 180a 250mcm al 205a voltage drop not a problem.
Slowpoke
01-23-2004 23:27:10
 Re: Re: Wire Size for Underground Service to Garag in reply to BIG WOOD , 01-23-2004 16:46:39
I'd use 3" schedule 40 underground electrical conduit for the run. Co-op will probably require a 24" or 36", 90* sweep at the pole and barn. Those sweeps are for the above UG sunlight resistant conduit only. Won't fit tile or sewer ABS.
Then from the sweep up to the meter box, use schedule 80 conduit. The sweep will not be exposed above ground. Only service cables in the conduit. Water lines at least 12" away.
Mark
01-23-2004 14:54:42
2/0 copper would be minimum with not very cold temps. If you are in a cold climate,1/0 copper and put either one in a conduit or a pvc pipe to prevent excessive voltage drop from wet soil/extreme cold conditions.
buickanddeere
01-23-2004 16:10:12
 Re: Re: Wire Size for Underground Service to Garag in reply to Mark, 01-23-2004 14:54:42
Wet soil and extreme cold does not cause voltage drop. Electrons do flow easier the colder the material(most) is however. Most areas need the burial depth to be 30+" depending on the usage of the ground above and type of conduit if any.
old
01-23-2004 12:15:21
I'd also say 2/0 no smaller and copper even if it costs more is worth it.
Bigdog
01-23-2004 11:55:59
Electric co-ops usually specify what minimums they require. Check with them as you will have to pass their inspection in order for them to connect you. I would think 4/0 would be required.
buickanddeere
01-23-2004 12:06:44
 Re: Re: Wire Size for Underground Service to Garag in reply to Bigdog, 01-23-2004 11:55:59
2/0 TWU copper. Best pulled through a conduit or 4" drainage tile. The meter base should be one made by Sommers or similar. It contains a transfer switch and plug for a standby generator. Isn't expensive and this is the time to do it even if you don't have a generator. Saves making those crude and dangerous welder plug back-feed abominations or vice grips in the disconnect box hack jobs. Eliminates back-feeds to the grid and maiming/killing linesmen. And eliminates the grid backfeeding your generator and letting the smoke out. Electrical equipment doesn't work after you make the smoke leak out. Simple for the wife,kids hired man or the man himself to transfer power without incident.
frank wi.
01-23-2004 17:13:33
 Re: Re: Re: Wire Size for Underground Service to G in reply to buickanddeere, 01-23-2004 12:06:44
your electrician has to size your electrical eq. to the state electrical code. your power co. will size to the etimated load.1/0 triplex ug cable will carry almost 200 amps for the distance. i would suggest 4/0 instead.in my state ,after the meter is cust.owned.so, it has to be ul approved and written in the insulaton,plus a second grd. wire. so your looking at four conductors in all. that second grd.wire does not have to be the same size as the triplex 4/0.might get by with#6cu. check code for sure. lot to size up. frank