WHAT SIZE OF ELECTRICAL WIRE TO RUN
len
07-25-2003 17:34:01
We have a shed on a piece of property with a 100 amp.electrical service and we want to run electric to our 5th. wheel that is 650-700 feet away from the service.
Was wondering what size wire would work for this would be running lights frig. and sometimes the air conditioner.
Also what is best above ground or buried want to use copper.
thankyou
andyd
07-30-2003 20:21:52
 Re: WHAT SIZE OF ELECTRICAL WIRE TO RUN in reply to len, 07-25-2003 17:34:01
The cost of The wire and connectors would make this cost prohivitive? the air cond will need 3 times its rating in amps to start ? the power company will put up hi voltage wire ,transfomer, all you need is service pole and fittings? belive you going to have a contract with them for couple years so they can recover their cost?but its the most econmy way and better on your air cond? serviced air cond for years and the biggest problem was insufficent wiring?
CNKS
07-26-2003 11:51:38
You have received a variety of responses, however the way to get the correct answer for your area is simple. Simply call your local city/county inspectors office. Remember that if you don't, and an accident involving your line happens in the future, you may be liable. If you have your electric company change out your meter to, say 200 amp, you can run your existing service and the added service with no additional minimum charge.
Gary in IL
07-26-2003 11:34:37
Len;
Why not have the power company run another feeder and put in a second meter ?
Any usage at all would cover the minimum meter charge, and no voltage drop or wire size worries !
DaveK(IN)
07-26-2003 08:17:30
The theoretical voltage drop calculations often yield impractical wire size requirements. For what you describe the # 6 or probably # 4 will work just fine. The big question is how to install it.
You may be able to order a 1000' reel of Type UF wire that would let you bury it without a splice. The depth required is only 18" per the NEC.
If you are going to invest in the trench, I would put in conduit at least 1 1/4 " and put a pull box midway. This only has to be 12" deep. This is a long pull and you may want to get professional help if you aren't experienced with this.
Here's one more idea- Put a small trailer service in where you park the rig and let the power company string the line and eat the voltage drop. The minimum meter cost is probably $ 15 or less per month. Do the math and see how long it would take to pay for even the material for your own line. Plus they do the maintainence.
Good luck with your project.
Green_in_MI
07-25-2003 19:49:17
For a 2% voltage loss for only a 20 amp load at 120 volt single phase you will need a 2/0 wire guage. I would not be surprised if that cost you a couple dollars per foot and i don't think that is enough wire to carry all the current you want to. You might want to look for a different solution for your electrical needs.
Use----
07-25-2003 19:45:26
#6 U.F. wire butied at least 3 feet deep.