Load
dg
04-03-2003 06:05:29
Can someone tell me how many amps a 1hp motor pulls at 240 volts. Thanx
Chris
04-06-2003 08:08:03
 Re: Load in reply to dg, 04-03-2003 06:05:29
Go a bit large on the wire . You might want a light and an outlet in that well house!
David - OR
04-03-2003 07:32:20
1HP is about 750 watts. Simple unit conversion.
Watts = Volts * Amps
At 240 volts and about 80% efficiency figure 4 to 5 amps running current.
Starting the motor under load is a different story. Motors can draw 3 to 5 times their running current (or more) on startup, until they reach their normal running speed. This can be an issue if you are thinking of driving the motor with a generator of limited capacity.
dg
04-03-2003 07:49:11
 Re: Re: Load in reply to David - OR, 04-03-2003 07:32:20
Thanks Dave, I'm looking into having a well dug and it looks like it's gonna have to be a ways from the house. Just priceing wire for voltage drop.
G Taylor
04-04-2003 11:47:35
 Re: Re: Re: Load in reply to dg, 04-03-2003 07:49:11
On that single phase motor the .6 or so power factor will increase line current to about 8.0 amps. #12 will be ok for a about 175 ft with 3% vd. Check voltage at the panel, sometimes only 110.0v line to neutral will be available. Not much room for error unlike a service with 125.0V line to neutral.