Yesterday's Tractor Co. Affordable Parts, Just in Time
TRACTOR   PARTS TRACTOR   MANUALS
   Allis Chalmers Case Cockshutt Farmall IH Ford 9N,2N,8N Ford
   Ferguson John Deere Massey Minn. Moline Oliver All The Rest
Tractor Manuals
TractorLinks.com
Enter your email address to receive our newsletter!
subscribe
unsubscribe
Tractor Talk Discussion Forum
Topic: Water Well pump/wire problem
[Return to Forum]
John in La
02-15-2013 20:31:49
184.38.196.203
My 220 breaker for my 1hp deep well pump is tripping. It will not trip right when you turn it on but after 3 or 4 minutes it trips.
I threw some parts at it last night (new breaker and new pressure switch) trying to take the easy way out but that did not help.
Tonight I took the wire loose at the pressure switch; put wire caps on the ends of the wire and turned on the power. After about 5 minutes the breaker tripped.
So now I assume the wire has a break somewhere. Problem is it is 250ft long and buried about 1ft deep in the hard clay for the past 13 yrs.
Unless someone can give me some advise on how to narrow down where the problem is so I can fix it I guess I am headed to the orange box store in the morning to buy some wire.
Southwire 250 ft. 10-2 UF-B W/G Cable $224.00
[Reply]   [No Email]
George Marsh
02-16-2013 11:26:36
50.104.195.160
Re: Water Well pump/wire problem in reply to John in La, 02-15-2013 20:31:49
John,
If this has worked for 13 years, I would first get the ammprobe out and measure the amp draw. If the amp draw is what it should be, I would then take a look at the breaker. Breakers work on temperature. If there is a bad connection where the wire screws on the breaker or where the breaker connects to the buss bar it will cause the breaker to trip when it shouldn't.
Why do you have a 1 hp pump? How deep is your well? Can you get buy with a smaller pump and not change the wire? Is it possible your pump is going bad and not a wiring problem.
My well is 75 ft deep, water table at 30 ft and I get 12 gallons per minute with just a 1/2 hp pump. Uses a tick over 10 amps on 120v.
George
  [Reply]  [No Email]
4020guy
02-16-2013 10:09:15
68.171.72.108
I agree with Rod. Go with #8 MNWU inside some PVC down 3 feet and be done with it. Say someday you need a larger pump motor. Cutting corners generally comes back to bite later on. If you were doing 100, the costs would add up but you're only doing one, yours....Ron
  [Reply]  [No Email]
RodInNS
02-16-2013 09:05:44
216.118.158.123
Wires must have got corroded/wet. DO you know what it's actually drawing for sure? Be kinda nice to know that just to rule out a bad breaker?
I'd be highly inclined to run an 8 for that load at that distance... I think ours are buried inside 1" black poly. Dunno how code applies to that but that's how it was done 35 years ago...
Rod
  [Reply]  [No Email]
mike nh
02-16-2013 08:31:33
75.67.97.215
You should be able to run a 1hp pump up to 400ft total on #10 wire
  [Reply]  [No Email]
John in la
02-16-2013 08:17:29
184.38.196.203
OK here are the specs off the motor.
1hp
Max load amps 14.8/7.4
I am running it on 220 so (I assume) pulling 7.4 amps max
Wire run is just under 250ft
I would think 10 gausge is enough but you tell me.
  [Reply]  [No Email]
john *.?-!.* cub owner
02-16-2013 20:06:04
207.119.216.44
Re: Water Well pump/wire problem in reply to John in la, 02-16-2013 08:17:29
John, if your wire runs under a road a rock has probably worked through it from vehicles driving over.
  [Reply]  [No Email]
Janicholson
02-16-2013 07:26:40
74.60.94.18
I agree with John T and others. If it trips when disconnected on the load end it will need to be replaced. Were it mine, I would dig it up in the center of its length (less digging than all the way) and use an amprobe meter on the wires If it shows current when the breaker is on, the short is farther, if none, it is nearer the house. Repeat to find the short. (an amprobe needs to be placed on one wire only IIRC)
I also think 250 feet is too long for 10 gauge wire on 1 hp load. Jim
  [Reply]  [No Email]
John in la
02-16-2013 07:59:18
184.38.196.203
Re: Water Well pump/wire problem in reply to Janicholson, 02-16-2013 07:26:40
So do you all think I should upgrade to 8 gauge.
Want to do it right so I never have to mess with this again.
I can not find 8/2 UF in stock today but one place has THWN 8 gauge. I understand the THWN will have to go in a pipe.
I can get the specs off the motor if that helps.
  [Reply]  [No Email]
js305
02-16-2013 06:53:27
184.79.57.233
Neighbor had a similar problem, no money to spend on someone to come out and find the short. I went down there and noticed her dog had been digging in one place after a rain. I killed the power and disconnected both ends of the buried line (about a hundred feet) and helped the dog dig and found a bad place. Fixed that and for now the problem is solved. I suspected a gopher or some other critter and figure the whole thing needs replacing though. The dog was evidently "hearing" the short and curious.
  [Reply]  [No Email]
oldfarmtractor
02-16-2013 06:52:04
71.155.240.88
Check the voltage at the breaker and then the pump while the pump is running. Low voltage makes for higher current.
If that is all cool, then try running a set of wires above ground for a test. You may find that your pump is tired.
  [Reply]  [No Email]
John in la
02-16-2013 05:41:19
184.38.196.203
This is a above ground 1hp jet pump. The pump; water tank; and pressure switch are all in a 4x4 pump house in my yard.
The wire runs to the main fuse panal on my house and this is where the breaker is.
I have replaced the breaker and pressure switch with new but that did not help.
I am using 10-2 UF-B W/G direct bury wet location wire and it is in conduit from the fuse box in to the ground and again where it comes out the ground and up the side of the pump. Each conduit has a long sweep 90 on the bottom in the ground so the wire runs straight out rather than bending around a corner. I just do not understand how a wire can break buried in the ground.
One question I do have now.
Someone suggest I put the entire length in conduit. Do I still have to use direct bury wire with conduit.
I can get Orange 10-2 Romex NM-B W/G Indoor Wire and enough conduit to do the job for about the same money. Would this be OK to use???
  [Reply]  [No Email]
John T
02-16-2013 06:42:44
71.52.99.130
Re: Water Well pump/wire problem in reply to John in la, 02-16-2013 05:41:19
Im rusty as an old nail on the latest Code, but best I recall you can use direct burial rated cable like (UF Undergroud Feeder) or if you wanna bury conduit you can use individual enclosed THWN rated wires. The W in THWN versus say THHN wire is for wet locations as I recall. Of course just trenching in UF cable is easier but Id go deeper then only a foot, warning tape above the cable isnt a bad idea. Plastic conduit is permissible unless under driveways and it needs to be rigid or IMC when it comes up above the ground and enters a building..........
If shes tripping a breaker even when opened and capped of at the pumps end, must be a bad/shorted/chewed cable well DUH
Have you calculated voltage drop at your load?? If necessary you may need to increase wire size??
John T No warranty Im rusty remember
  [Reply]  [No Email]
MarkB_MI
02-16-2013 06:16:46
75.198.122.191
John, if you lived where frost is a problem, I'd say the problem was caused by earth movement. But since you're down south, I'd guess you have critter problems. A foot deep is barely enough to avoid gophers, moles and ground squirrels; if there's a spot where the cable is a bit shallow then it would be vulnerable. Bury it deeper and you should be OK. You also want to make sure there are no rocks in the trench. Even if you don't have frost, vehicles driving over the cable can cause problems if the cable is in contact with a rock.
I don't believe you can use Romex underground even if it's in conduit. It's still a "wet" location, since any water that gets into the conduit won't be coming out. I sure wouldn't skimp on something I have to trench in.
  [Reply]  [No Email]
John in la
02-16-2013 06:58:32
184.38.196.203
Re: Water Well pump/wire problem in reply to MarkB_MI, 02-16-2013 06:16:46
Thanks Mark
Called the orange box store and they have a 6in wide by 36in deep trencher for $150 a day that comes on its own trailer. That ought to get me down deep enough.
Looks like I have a busy weekend ahead. Better get after it.
  [Reply]  [No Email]
MarkB_MI
02-16-2013 07:10:59
75.198.122.191
Re: Water Well pump/wire problem in reply to John in la, 02-16-2013 06:58:32
Hi John,
I've used one of those smaller Ditch Witch trenchers, and they'll get the job done. But it will be a workout to trench 250 feet of wet clay, especially if you have any tree roots to deal with. (I'm assuming that in LA, wet is the only variety of clay you have.) I see that the nice man in the picture happens to be trenching in dry sand; you may not have the same expression on your face when you're behind that trencher. Make sure they show you how to engage the differential lock. Also, I happened to notice that our local HD had the chain backwards on one of its trenchers, which I'm sure made for great fun for the next guy to rent it!
  [Reply]  [No Email]
evilboweivel
02-16-2013 05:04:31
75.185.40.180
clamp an amprobe on at the panel with the wires capped off like you have them now.
any amp draw equals bad wire
no amp draw change breaker
also wire should be buried 30" minimum
good luck
  [Reply]  [No Email]
El Toro
02-16-2013 04:57:38
108.3.143.30
I would try another breaker of the same amperage
as been suggested. Hal
  [Reply]  [No Email]
nys
02-16-2013 03:35:58
98.15.254.212
If you decide problem is in the wire underground my electrician friend has a testing device he used to find a break in the undergroud to my shop. Just dug it up at break and spliced it. good luck
  [Reply]  [No Email]
Bret4207
02-16-2013 04:56:34
64.19.90.196
Re: Water Well pump/wire problem in reply to nys, 02-16-2013 03:35:58
Had the same problem. Mine was a break underground between the pressure tank and well casing. Caused all sorts of problems- like stray voltage in our pool! I've seen the wire get worn through with submersible pumps too.
  [Reply]  [No Email]
MarkB_MI
02-16-2013 03:30:41
75.219.162.73
I don't think you'll be able to find the short with instruments you're likely to have at your disposal. If it failed after only 13 years, I'd say it wasn't buried deep enough and it's likely to give you more trouble in the future. You might try first hand-digging around where it enters your house and pumphouse since you'll need to do that anyway to replace it; maybe you'll luck out and find the problem.
  [Reply]  [No Email]
ohiojim
02-16-2013 03:27:53
50.126.220.130
like old said, there is usually enough wire at the well to come above the caseing, you could cut it there if they left you enough to reach, then put splice kit on after
  [Reply]  [No Email]
TractormanNC
02-16-2013 03:21:51
108.72.58.200
I assume you have direct burial wire.
Buy some PVC conduit and put the wire in it. You will probably never have another problem unless someone cuts the conduit. If you do have a wire problem, pull out the old and pull in new wire.
  [Reply]  [No Email]
John in Md
02-16-2013 01:26:13
70.192.196.30
Go to your breaker box and switch your well pump breaker with another 220 breaker of same amps, see if it makes a difference. I had a 20 amp start tripping on its own, they don"t last like they use to.
PS It was a square D.
  [Reply]  [No Email]
John in Md
02-16-2013 01:26:12
70.192.196.30
  [Reply]  [No Email]
huntingreen2day
02-15-2013 21:49:00
75.131.120.19
I have seen the wires damaged that run down the well to the pump.
  [Reply]  [No Email]
old
02-15-2013 21:04:10
209.86.226.27
Well from what you say sounds like the pressure tank and switch is at your house but the well is 250 from the house right??? If yes is there a way to unhook the pump from the wire and then turn things on and see if the breaker trips?? Because if you can do that you can figure out if the problem is in the wire in the ground it the wire down the well. Reason I say this is a few years back I had a problem like that and found that about 3/4 of the way down the wires had rubbed and shorted out in my well so I had to replace the wires from the pump up to fix it
  [Reply]  [No Email]
[Options]  [Printer Friendly]  [Return to Forum]   [Add a Reply]
Same-Day Shipping! Most of our stocked parts ship the same day you order (M-F).  Expedited shipping available, just call!  Most prices for parts and manuals are below our competitors.  Compare our super low shipping rates!  We have the parts you need to repair your tractor.  We are a Company you can trust and have generous return policies!   Shop Online Today or call our friendly sales staff toll free (800) 853-2651. [ More Info ]
Copyright © 1997-2013 Yesterday's Tractor Co.
About this site - Yesterday's Tractors is your one-stop source for antique tractors. If you are interested in older tractors you've come to the right place! Join more than 275,000 other classic tractor enthusiasts from all over the globe. We have many resources for antique tractor enthusiasts available including photos, classified ads, more than 24 tractor discussion forums, a show guide, values, specs and much more. Bookmark this site and come back often. Thanks for stopping by! Feel free to use our feedback form to send us your comments, suggestions and ideas.