Yesterday's Tractor Co.
Shop Now View Cart
TractorLinks.com
Tool Talk Discussion Forum
Re: Transfer switches
mazemeister
08-04-2013 15:49:55
True, you only NEED a two pole transfer switch, but my thinking is, it's better to switch the neutral also. I've heard of the utility workers switching a hot and a neutral on the pole and burning down houses!
any reason not to use a 3 pole, double throw switch before the panel and be done with it?
John T
08-05-2013 06:01:14
 Re: Transfer switches in reply to mazemeister, 08-04-2013 15:49:55
The Utility Neutral has a tie to mother earth ground at the pole and theres another tie to mother earth ground at the service entrance so thats not a hazard.
If the genset is NOT configured as a Sepreately Derived Source, the 2 pole xfer swith is cheaper. Sure you can use a 3 pole and switch the Neutrals if the genset is configured as a Seperate Derived Source, but its more typical to use a 2 pole around here at least..
John T
buickanddeere
08-04-2013 18:19:15
If the generator has a bonded neutral, the transfer switch should switch the neutral as well as the live lines. If the generator has a floating neutral , the transfer switch should not switch the neutral and only switch the lines. Running neutral current on the ground system will shock livestock . Cause problems with communication equipment as land line phones, cable TV communications , alarm systems etc.