TractorLinks.com
Tool Talk Discussion Forum
Re: Sub Panel Question
Plane Bart
11-17-2012 08:53:40
If the panel will be located right next to the main panel you can use a 1 1/4" off set nipple as long as the cover of both panel will open you will be fine.
You can use PVC electrical conduit also for more space if needed.
Get the Plastic bushing to protect the wires.
# 6 THHN is required for 60 amps
You can use all #6 and phase tape them or buy #8 Green THHN for yor ground
Line 1 black
Line 2 red
Neutral white
Ground green continuos green insulation or phase taped green on end to the other.
Do not bond ground and neutral in the sub panel
You must have all grounds and neutrals separated on steppe rated ground bar neutrals will be isolated from ground and go on the neutral bar ground bar will be purchased sepperlaty
And gets mounted to the panel enclosure
All 240 volt circuit comming from the sub panel will need to have two hots a ground bare copper a separate insulated neutral conductor Bart Master electrician