Re: Portable generator not generating power
Den N Ms
12-16-2012 15:06:39
TO CHECK CAPACITOR
(if generator will not re-excite)
1. Remove end cover screws and end cover
from genhead. NOTE: The capacitor on the
GHC6510 and H650CS is located in the panel
assembly, see To Remove Panel Assembly for
this unit and proceed.
a. Remove capacitor leads.
b. Connect VOM to capacitor and watch for
low ohms reading that slowly progresses
to an open circuit. Open circuit from beginning
indicates bad capacitor.
TO CHECK STATOR
(if generator will not re-excite and capacitor is
OK)
1. If the capacitor checks okay, check for open
circuits in stator.
2. To check for open circuits in stator,
attach VOM to the following leads:
A. Black- Orange
B. Red- Green
C. Pink capacitor lead- Pink capacitor
lead
Open circuit indicates bad stator.
3. If open circuits are not found and there is
still a problem, check for circuits grounded
in stator. Attach VOM between:
A. Black- Stator laminations *
B. Red- Stator laminations*
C. Pink capacitor leads- Stator laminations*
No reading indicates good stator. No reading
will be indicated on meter as OL.
4. Attach Vom between black and pink capacitor
lead; and red and pink capacitor lead.
Your reading should be infinity or OL. If you
read zero or above, this indicates bad stator.
Most commonly caused by lacings meshed
between windings as shown.
* Varnish on the laminations must be
scraped off to make contact with the
metal surface for correct readings.
TO CHECK ROTOR
(if generator will not re-excite and Stator is OK)
1. If stator checks okay, then check rotor for
open circuits. If the rotor has two diodes,
remove one diode and attach VOM to solder
junction of removed diode to solder junction
of the remaining diode. Open circuit indicates
bad rotor. If the rotor has one diode, remove
the 1/4"-20 nut above the 1/4" female connector
and remove from diode bracket.
Attach VOM to female connector and solder
junction on diode. Open circuit indicates bad rotor.
TOM N MS
12-16-2012 16:04:00
 Re: Portable generator not generating power in reply to Den N Ms, 12-16-2012 15:06:39
Den, thanks for the info--if some of the easy tricks don't work I'm going to tell him to return it to its owner and let them get it to a shop. Have you seen the one where u make a cord up apply 110v?
Den N Ms
12-16-2012 16:18:26
 Re: Portable generator not generating power in reply to TOM N MS, 12-16-2012 16:04:00
You mean hooking it to 110 volts?
NO! DON"T DO THAT!
TOM N MS
12-16-2012 17:33:13
 Re: Portable generator not generating power in reply to Den N Ms, 12-16-2012 16:18:26
I"m not telling others to do it but sounded interesting and if I was having trouble I"d try it..